No heat w/new-ish Buderus boiler
Lil-Roc
Have a Pro come out. More likly pilot oriface is plugged with soot. I'd start there then check gas pressure,then gasvalve itself. Again have a Pro look at it.
no heat w/newer buderus
Hello Gents:
Homeowner here--been on the board before with questions about a poor changeout of a Buderus G124x, standing pilot. I've had various troubles with it (aquastat, autodamper, etc) but generally it's run OK.
My problem now is that the pilot went out sometime yesterday--no wind, gas outage, or anything --seems like it just went out.
Now, I can't keep the pilot lit.
Unfortunately, I got the short end of the stick on the install (their piping/sizing and such was heavily panned on the Wall.
Nobody else seems willing to service Buderus in my area, and I really don't want to call the people who made such a mess of the original install. But it's getting cold!
As I said, pilot won't stay lit. There is gas, nice blue flame when pilot button on the Honeywell valve is held down. Soon as I let go, it's out.
Main power fine, 24 Volts all the way to valve assembly. Thermostat calls for heat, and I hear the click when it does.
I guess this is probably the thermocouple? It's only four years old, but seems most likely?
Anyway to temporarily over-ride it so it will fire until I get help?
How hard a fix is it?
Thanks for any help you can give...I'm trying to make the best of a bad situation.
mike
General Info:
Buderus G124X25 Gravity conversion, hot water system. One zone only to old fashioned rads. Four years old.
Original Aquastat failed within a year and was replaced with a simpler Honey L8148J. Flue damper glitches resulted in damper being disconnected too.
Gas control valve is Honey VR8200H1004
thermocouple
most likely the thermocouple...its easy to install ...theres usually instructions on how to install it. but like the other guy said about the orifice in the pilot assembly and to check gas pressure you should have a pro come outASM Mechanical Company
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
How far in to the BOONIES are you???????
The thermocouple on the Buderus and quite easy to do, but you should be a pro. Worst case, get a good local, heating or plumber company ...they'll be more than capable. Mad dog
- 133 Chimneys & Flues
