4 taco valves w/ 50va transformer

james capaldo
Member Posts: 1
just added a forth zone to my house.Replaced the old 40va trans with a 50.Wired just like the old.Three zones wiork perfect.One zone is wild Valve opens when the boiler fires and will not shut off.The others work fine.Do I have a bad head or is there a differant way to wire the 4 zones other than diagram on the valve head.Taco shows using 2-40's.I used 1-50.I think the wiring must be the same or am I wrong.Thanks
0
Comments
-
(message from Antarctica) Here's the simple math. Multiply the amp draw of one valve (they're all the same, right?) by 24V for the VA of one valve. Then multiply that by 4 for 4 valves. That needs to be less than your 50VA.
Then make sure that your new valve is in a circuit made up the valve, its thermostat, and the transformer. The other valves and thermostats connect to the same transformer, but not to anything else.0
This discussion has been closed.
Categories
- All Categories
- 87.1K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 58 Biomass
- 427 Carbon Monoxide Awareness
- 117 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 111 Geothermal
- 163 Indoor-Air Quality
- 3.7K Oil Heating
- 72 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 55 Water Quality
- 49 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements