Unwanted vacuum in steam system
have the reverse check valves and they may be stuck, I have seen that happen especially on old systems.
I have 3 low pressure steam water tube boilers operating at 12 psi. They feed a heat exchanger w/ 2 motorized valves and 6 roof top heating units.
The 2 motorized valves on the heat exchanger are rated at 1/3 and 2/3 inlet.
When the lead boiler shuts off the entire system goes into a vacuum 4"w.c. to 5"w.c. and sucks water out of the boiler as the water level drops to the minimum level after the burner goes off. ( The burners are not over fired and the traps are working )
I did isolate the heat exchanger and have narrowed the problem to it.
Does anybody know why the heat exchanger is causing this problem?0 -
It is not the Heat Exchanger...
Well, actually it is, but it is not it's fault!
You need a vacuum breaker.
Vacuum is a normal occurrence with the collapse of steam- you want that for that is a creation of the steam giving up it's useful heat. You just have to accommodate it.
Nearly every shell and tube heat exchanger I have ever seen has a tapping for a vacuum breaker. Some old-timers used two horizontal check valves in series, aiming into the vessel. (Usually small, about 1/2" or 3/4", it does not take much and this depends on your vessel size and tapping size of course.)
You could do that or install a bona-fide vacuum breaker made for the purpose. Personally, I like to elevate them to above the HEX inlet flange to avoid a flood-line condition.
Now, for that matter, ALL of your steam consumers should have vacuum breakers, especially the air coils on the RTU's. Easy to freeze if you do not.0 -
A perfectly fair
observation and one reason I specify proper VB's. At the very least, the check valves should be brass or bronze- but you make an excellent point.
Speaking of which, a good pencil may solve it for the moment..0
- 50 Industry Classes