replacement radiator
Options
Garbear
Member Posts: 19
I'm replacing an old 4 tube 3' high radiator with a new 6 tube 25" high one to accomadate a new window.It is a 2 pipe hot water system and the radiator supply and return is piped on the same side high and low tappings. The manufacture spec sheet does not show that arrangment.
Will it work?
Will it work?
0
Comments
-
Will it work?
It will work fine. Pipe your supply to the top tapping and your return to the lower tapping.0 -
Thank you0