Question for Bill W@Honeywell
mtfallsmikey
Member Posts: 765
My wholesaler rep and I were confused looking at the catalog the other day...Looking for an angle mount TRV, 3/4" sweat, actuator on TRV, no remote sensor, mounted in BB. V2043ESL20 looks like the right one.(??)..help!
Hi, Mike.
The valve you mention is available as straight, vertical and horizontal body patterns. It is for steam only. The V2043ESL20 is a vertical body 3/4", female NPT inlet, male NPT outlet. You also need the SA143 steam vent, and a T100 or 200 series acuator. Check out www.customer.honeywell.com, scroll down to the lower right, mand type in the part number. You will get a PDF file of the tech sheet for this product. No charge and no password required.0 -
Oops!
Sent that too early this morning...I need a TRV for HW baseboard, 3/4" sweat/ threaded, angle...so I can have the sensor outside of the baseboard enclosure, but not a remote sensor...can you recommend what I need??...thanks, MFM0 -
Here's the closest I can come
This is a 3/4 angle pattern hot water valve, sweat fittings. Part number is V2040ESL20. The operator is a T100C1026, which has a remote sensor(inside the baseboard) and remote setpoint for mounting outside the baseboard. See pages 212 and 221 in the 2006-2007 catalog for more details. Also see page 222 for a mounting picture. This combo is designed for tight spaces. I hope this is what you need, check it out, and if you need more info, drop me an email.0