D.O.E.Capacity or I.B.R?
mjj_2
Member Posts: 22
A little bit of education is indeed a dangerous thing. In the process of picking a contractor to replace the old hot-water oil boiler in our 80-yr-old house CI-heated house,I'm contemplating 3 heat loss numbers. 77,280 BTU's calculated by one contractor, 97,850 by an energy audit rep. and 94,900 by me with HVAC-Calc (which apparently doesn't have a buffer-factor). None of these include the unheated basement.
My question is: should I be matching the heat load to the D.O.E. heating capacity or the IBR ratings? Our mains are insulated with intact asbestos.
Any advice is appreciated
In my opinion
stay with the lower #s, these are based on worst case scenario for your area so you will be fine.
Dave0 -
I agree with Dave
I=B=R ratings add 15% fat in what is probably already an oversizes system. You are not likely starting from a dead cold start. Use the DOE or AGA gross output number. It can save you a boiler size."If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0