Weights on the barametric draft control
 
            
                
                    Paul Fredricks_3                
                
                    Member Posts: 1,556                
            
                        
            
                    Where are you measuring the draft? -.02 should be over fire, not in the breach (smoke pipe).                
                0                
            Comments
- 
            Changing the weights
 I am doing the combustion analyzing, and my draft is 0.05 inches. Burnham recommends 0.02 inches. I have the weight adjusted all the way in. I can hold the door open farther to achieve the 0.02, but the weight is too heavy. Can I buy a smaller one or do I have to get out the fishing weights?
 JakeThere was an error rendering this rich post. 0
- 
            
 Yes, over the fire.
 JakeThere was an error rendering this rich post. 0
- 
            
 put in a second draft damper to solve your problem.0
- 
            Either a second damper
 as 3lees says, or replace the existing damper with the next larger size. Generally you can use a damper one size larger than the flue pipe diameter.
 That chimney was designed to pull draft thru the coal bed in an old coal boiler. On oil or gas it's way over-designed, so we need more draft-regulation capability.
 Excessive draft will pull the heat right out of the boiler. It could also pull pets and small children to the roof, so keep them away ;-)
 That draft spec over the fire is correct for a V-75. On a Mega-Steam you want a slight positive draft over the fire, and a zero reading at the flue outlet.
 To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
            Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 427 Carbon Monoxide Awareness
- 118 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 112 Geothermal
- 164 Indoor-Air Quality
- 3.7K Oil Heating
- 73 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements