The Taco PC700-2 will modulate the boiler to deliver the water temperature required to satisfy the load, based on outdoor temperature. However, if you have a non-condensing boiler the PID microprocessor has to start the curve from the minimum operating temperature typically set at 140 degrees. You’re saving are greater when using a condensing type boiler. Obviously, anytime you can reduce the water temperature of the boiler, you will save. How much is the variable.
Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions

Comments

  • Don_186
    Don_186 Member Posts: 7
    installing Taco outdoor reset control

    I have a pretty new boiler with 6 zones and a Taco 6 zone switching relay control. It looks like I could install a Taco PC700 outdoor reset control which would vary the boiler temp based upon outdoor temp. There are some other options, such as a purge control that pushes all the hot water to the priority zone when the burner shuts down. Are these add on controls cost effective?
  • Don_186
    Don_186 Member Posts: 7
    or go with Buderus Logamatic

    Since this is a Buderus boiler I could go with a Buderus Logamatic control or a Techmar I guess.
  • Will_5
    Will_5 Member Posts: 85
    Taco Reset

    I don't install Buderus but I install many of the Taco 700 controls, they are simple to install and there is no wiring exept for the sensors, you are generally going to have a switching relay anyway. I have yet to return to any job I have installed one for a problem. I'm sure the Logamatic is a great control and has a lot of great fuctions, most of the jobs I do would never utilize most of the functionality of that control.

    C
  • BillW@honeywell
    BillW@honeywell Member Posts: 1,099
    Take a look at our new Aquatrol unit

    We offer outdoor air temp based reset, 4 zone modules that will accept either pumps or zone valves, true priority for an indirect, communicating thermostats and a host of other cool features at a very competitive price. All packaged in an attractive black & red console that is VERY easy to wire and service. Programming is very simple, and once set up, will not be lost if the power goes out. This is just the start...much more coming soon. For more info, go to www.honeywellwaterawareness.com
  • jackchips_2
    jackchips_2 Member Posts: 1,337
    Bill

    you need to add an e in awareness.

    Jack
  • BillW@honeywell
    BillW@honeywell Member Posts: 1,099
    Thanks for catching that.

    I fixed it!