super store controller question
allenh
Member Posts: 117
Have a bad L'Aquarius controller that sits inside a super store. I cannot find this controller anywhere. What is a decent replacement controller to use?
It has the temp sensor that sits in the well, and has 2 sets of isolated contacts.
TIA
TIA
What for?
What is it that you are going to controll;
Sounds like maybe a setpoint controller?
Maybe Tekmar;Johnson controlls;Honeywell; just to name a few.0 -
This controller:
Is powered by 115 volts and NOT 24 v.a.c.;
adjustable hot water setpoint where I am looking for @ 125 F for domestic hot water;
Has a delta setting for setpoint;
has 2 relays with a common, n.o., n.c.;
One relay closes for T & T to call in boiler;
Second relay has 115 volts on common which closes to bring in Taco circ pump.
Setpoint/ Relay.
You could just use a Johnson A419ABC-1C setpoint control with a taco SR 501 or a RIB Relay.
OR:Maybe Honeywell has something try Asking The Control Goddess Carol Frey
Hope this helps Richard0
- 86.8K THE MAIN WALL
- 56 Biomass
- 106 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 104 Geothermal
- 69 Pipe Deterioration
- 953 Plumbing
- 385 Solar
- 15.3K Strictly Steam
- 43 Industry Classes
