Hydronic radiant heat in a 10 \" slab.
Uni R_3
Uni R_3 Member Posts: 299
  • Cindy Bodensteiner
    Cindy Bodensteiner Member Posts: 4
    I am in the process of negotiating for a hydronic radiant heat system in a new 2000 sq. ft construction. Due to earthquake requirements in the area, the foundation slab is 10 inches thick. I have contacted three radiant heat contractors in the area, none of which have put heat systems in that deep of a slab. Does anyone have suggestions about how to do that? How do you keep the tubing in the top 2-4 inches of the pour? Can anyone recommend a literature source that I can refer to regarding this issue? Thanks for your help!
  • kevin coppinger_4
    kevin coppinger_4 Member Posts: 2,124
    It is important...
    w/ that thick a slab to keep it in the middle part of the slab. This is done by using Chairs. Chairs are bent rebar that when installed will keep the steel mesh in the upper part of the pour...kpc
    The general contractor's concern is how can they walk on the area to perform the necessary tasks while the cement is being poured if the wire is elevated? They are using a crane type piece of equipment to deliver the cement via a shoot. I'm assuming the laborers will need to guide the tube in the area of the foundation forms as well as smooth and tamp the cement.
  • G.Kaske_2
    G.Kaske_2 Member Posts: 30
    Over the top
    What is speced out for the slab reinforcment cindy?
    An over the slab type system may be more efficient,for the pouring of the slab(pumped I believe your discription), and over all radiant system response/efficiency.
    There are a few products out there for over the slab applications. You just have to plan them into the design.
    Raupanel, Roth panel, Warmboard, sleeper system Gordy
  • Tony_23
    Tony_23 Member Posts: 1,033
    My opinion
    If the concrete contractor doesn't know how to work around "chairs", get a different concrete contractor.
  • Brad White
    Brad White Member Posts: 2,399
    Some Thoughts
    Can you move? :)
    Sounds like a serious project. Where is it -and can I guess? The climate is key. If Northern CA or the Pacific NW you have a steadier climate -better considering the mass you will have- than our eastern roller coaster of late.
    The Radiant Panel Association is one source of information.
    http://www.radiantpanelassociation.org/i4a/pages/index.cfm?pageid=471
    John Siegenthaler and Robert Bean are both authors and sources not to mention resources in affilliation with the RPA. The work of both should be sought.
    Setting the depth is done using chairs or stand-offs supported from the substrate or from the welded wire mesh. Might slab that thick may have two layers of mesh allowing the upper one to support the tubing matrix? Ask your structural engineer. I am assuming that this has to be monolithic for structural reasons. That said, might you consider a topping slab over the structural base? Will change your detailing but will keep the structural pour intact and give you a choice of floor finishes.
    From a controllability standpoint, you understand I am sure that you will be warming up all of that concrete eventually. Part of me says, the deeper you are the more even the surface temperature and that is a good thing. If I had to punt I would say the middle of the slab but will leave this to more hands-on practitioners than I. The other part says, once warm you will not be able to shut it off right away. How much solar gain the space has will be a huge factor.
    The reason I am waffling on the depth is, if the tubing is in the upper few inches of the slab, the slab beneath the tubing has to be warmed too, eventually anyway. You will get heat to your space faster but the boiler will run longer until the full mass heats up. Thus the center gets the nod to my thinking.
    I would put it before the group, others with far more experience than I, what they would do.
    Spend money on good anticipatory (PID) controls. Monitoring the slab warming/cooling rate over time relative to room temperature is critical. Little sips of tepid water over time. What you pump into your slab on Monday may not show up until Wednesday...your slab will weigh 117 lbs. per SF.
    From a constructability standpoint my initial concern is the curing temperature of all that concrete. Not sure how hot it gets with that deep a pour compared to what PEX can withstand (180F and up). I personally would use PEX-AL-PEX (aluminum cored pex) for the higher pressure and temperature ratings. Also should the O2 barrier be abraded by the concrete, the aluminum is the barrier ultimately.
    Anyway, sorry to ramble. I think I identified more problems than solutions... alas, it is late.
    "If you do not know the answer, say, "I do not know the answer", and you will be correct!"
    -Ernie White, my Dad
  • G.Kaske_2
    Depends does'nt it
    Key here is what is specd for the slab reinforcement as to what is being chaired up.
    If its wire mesh it could prove to have undesirable results unless you chair the living crap out of it. Remember you will have laborers, finishers tromping all over it, 5" to chair up mesh is asking alot to keep it where you want it.
    Rebar #5 12" on center longitude, and transverse would be an ideal scenereo to work with, less chairing needed with a more rigid structure to mount tubing to.
    Doing something over the top would solve all the problems of mass, respose, and cry babying.
    When properly cured 10" of concrete should not generate over 85 to 90 degrees worth of heat depending on time of year maybe 100.....Key there is when PROPERLY CURED.
    Gordy
  • Ed_26
    Ed_26 Member Posts: 284
    insulation
    Don't forget the insulation! (under the slab)
  • don't forget
    Don't forget to insulate the EDGES of the concrete.... One of the most overlooked and expenive mistake til its too late....
  • Weezbo
    Weezbo Member Posts: 6,231
    are you building on a fault line?
    Sell the property and move while you are still above ground.
    Find another engineer.
    bag the cement guy while you are at it.
    really, you seem to have the worst of all possible help, until you showed up here:)
    find someone who knows what they are doing to find you some incompetents to do the work.:) then you can blame him for everything that goes wrong.. and feel Good about it , knowing you weren't the person who hired them in the first place. That is so important in this day and age....having some one to whom to, firmly affix the blame...:)
    It would not do you any good to direct the work from an arm chair...let me say though that the Japanese have had many a chance to rethink building so have the Alaskans..i have experienced plenty of earthquakes and a 2000 sq ft structure to an earhquake, is something, were it made of solid metal, that would likely fair no better as to its condition or its whereabouts thereafter...just a thought ....though not very uplifting.
    i have poured some cement in my days, i happen to like slab on grade as a building practise. our most recent building has 3 foot wide Footing 16" deep with 16"X12"deep footings on the five transverse walls. the size is slightly 9X's the dimension of your slab. the depth of the slab is 4" over 2" of foam board.we drove some heavy equipment in to keeep it warm in 40 below...trust me on what i am saying....get some better help.
  • Constantin
    Constantin Member Posts: 3,796
    Cindy,
    I'd go with Gordon and Brad's suggestions re: tubing location. Unless you install the tubing on top of the slab with some insulation below (which is an option), that slab will eventually warm.
    Your biggest issue, IMO is not the depth of the slab, it's the responsiveness of the system due to the immense mass that is attached to it. On the one hand, that slab is going to be a wonderful thermal battery, on the other hand I worry about the heating system being able to heat said slab quickly enough to respond to quick changes in the outdoor conditions.
    In a well-insulated house, it'll be the lap of luxury and you may be able to go for days without power and yet not have the house freeze up. In a poorly insulated, leaky house you'll be cursing the time it takes the heating system to come up to temperature when a cold snap hits and the slab temperature has to rise in response to the increased heat loss.
    A two-pour approach makes sense for leakier homes... keeping the tubing close to the surface where it can respond more quickly to peak demands while preserving the deep slab below as a "baseline" battery. Unfortunately, thin slabs have two things going against them: they are prone to cracking (not an issue if you were planning on putting another floor material like wood on top of the slab) and there is the additional cost of a 2nd pour.
    IMO, insulation of the slab and the house will be the key to comfort and economy. Make sure that whatever radiant/concrete contractor you choose has the right ideas about edge details and insulation schedules to ensure that your home doesn't lose a lot of heat to the ground. The schedule of insulation depends largely on the location and the soil conductivity. Those fortunate enough to build in sand have less to worry about than those building in/on granite, for example.
    Insulation material is another important variable. We used XPS (Dowfoam) to great success here. In other parts of the country, even borate-treated versions of this sort of foam are frowned upon by building inspectors due to termite issues. Thus, call the BI and confirm what you can and cannot use.
    Your home insulation/architecture will be equally important. With a potentially slow-responding heating system, it will be key for comfort to reduce the "swings" in home heat demand by insulating the home well. The slower the rate of change, the easier a time the slab will have with keeping up and the better the "flywheel" effect of all that thermal mass.
  • What he said...
    Do it in lifts. First lift 6" thick, second lift 4" thick with chairs and WWM to hold the tube mid second lift.
    It will cost more due to mob/demob costs, but will be worth it. You have one chance to get it right, especially when poured in cement!
    And as every one else stated don't forget blue board insulation on bottom and edge.
    ME
  • Uni R_3
    Sandwich?
    Could this be done by doing the thick slab, then put the insulation down and then do a thin pour on top of that with the imbedded radiant? What would be the downsides?
  • Brad White_9
    Brad White_9 Member Posts: 2,440
    Structurally
    (and I admit this is not my primary area of expertise), the slab may have to be cast in one monolithic pour for structural reasons. Bonding and dowelling of the layers may be an issue and the diaphragm and "beam depth" inegrity may not be assurable.
    Otherwise, I agree, pour in lifts as you said, for shear constructability reasons.
    Naturally, Cindy's structural engineer can better advise her.
    My concern about temperature is the endothermic properties vary by thickness, sort of compounding. As Gordy points out, 100 degrees is not uncommon but that I associate with a 4" slab.
    When pouring a proton therapy facility, the three, four and sometimes six and eight foot thick slabs of hematite-embedded concrete took months to cool.....
  • Dale
    Dale Member Posts: 1,317
    thick slab
    First, a correcly insulated thick radiant slab is the best back up heat source for the money, with a new house you could be warm for a week in a power outage. I would check with the rad tub supplier about current placement and tube protection at break line reccomendations. I think the center suggestion is correct, me, I would just call wirsbo/uponnor.
  • G.Kaske_2
    Brad
    You are correct about the endothermic properties that is why I stated when PROPERLY CURED. I come from a more stringent spec. oriented enviroment. I have seen what commercial, and residential concrete can be subject to in the pour/ cure process.
    Heavy, and Highway construction standards on the other hand..... the testers, and RE's are always there to make sure things are properly done. While some think of them as a monkey on ones back they are there to insure a top quality product.
    Cindy is I'm sure up against a GC who has his own concrete contractor he uses all the time. Who wants to get in, get out, get paid with as little job related hassle as possible. Not sticking up for them merrily painting the picture.
    As far as the tubing in that particular slab yes its doable as everyone has suggested...but is it the best option? I'm thinking, and only guessing her climate maybe tempid being in a earthquake zone. So is all that mass plus added controls to keep the fly wheel effect at bay the best option for her, and everyone involved.
    Another option is ceiling radiant very delightful I must say.
    Gordy
    Fault Line
    I live in Northwest California Redwood country. We have temperatures in the 20-110 range, with most winter temps in the 30-50 range. The new housing development is near a very minor fault line, so minor, in fact, a new hospital is being built in the same area, approved by the seismic specialists etc. Alas, now you know, I want to walk to work! Thanks for all your input. I will present the information to the radiant heating contractor as well as the general contractor and see what they can figure out. I am doing this research myself to be pro-active in securing a heating system that I think is the most energy efficient, has the best warmth for heat and produce the least amount of internal environmental pollutants. Several other prospective homeowners in the new development have expressed interest in hydronic radiant heat. I think it will be in the best interest of the developer to figure this out! Thanks again. Cindy
    A decision has been made.
    Well, always a little slow on the information highway here! Apparently the slab is a new type called a "tensioned" slab that uses some kind of cables and a million pounds of tension to engineer the slab and that has something to do with why they can't put the tubing in the slab. The structural engineer demeed a 2" over-pour is the way to go. Warmboards were considered, but were cost prohibitive, even though they are manufactured across the street from the development! Thanks for eveeryones input. Cindy
  • jp_2
    jp_2 Member Posts: 1,935
    Need to be in slab?
    cindy, does the tubing need to be in the slab?
    could it be on top? as in warmboards or similar set up insulated from the basement floor?
    it would be a great benefit if you do NOT need to heat up all the concrete.
  • Brad White_9
    Had a feeling
    that was to be one special slab... Seems like that slab will still be there, warm and toasty, after a 9.0... how comforting is that? :)
    Ironic the proximity to the Warmboard factory!
    Now your challenge, Cindy, is the insulation. As stated, edges are critical but so is the downward mass. If that structual slab is at least edge insulated, I suspect an R-5 may be OK below your topping slab but will still add an inch. I would do R-10 given an ideal situation but then you have a 4" total topping depth. Even the additional 1" of an R-5 may be an issue for you.
    Good for you for going radiant. Keep in touch, send progress photos if you can.
  • Brad White_9
    Gordy
    I did get the properly cured part so was not a challenge (we agree totally). Just the notion of how one properly cures that mass and keeps the temperatures down in actual practice.
    Perhaps off topic but how hot would a 10" slab get compared to a 4" slab and compared to the PEX ratings in an ambient of say, 80 degrees? Ouch.
    The Proton Therapy pours (trucks around the block 24-7 for way too long) were uncomfortable to stand next to, let alone on. Talk about radiant... but very even indoor temperatures once cured...
  • GMcD
    GMcD Member Posts: 477
    Best heating system for your climate
    The best heating system for your climate would be a good envelope with a bit of passive solar, and some really good windows. With 20F outdoor winter design, and an HRV, you should be able to heat the house with a few lights and body heat if the envelope is done right. In fact, using low temperature panel radiators with a little modulating condensing boiler would be as efficient as the big radiant slab. If you are absolutely in lust with the warm feet feeling, consider using capillary tubes in thin-set mortar beds under the few hard tiled floor zones (bathrooms), or electric heating mats (NuHeat), and see if the Governator will give you some grant $$ for a couple PV Panels and solar water heating panels while you're at it!