changing blower speed
JR_7
Member Posts: 2
I would like to lower the blower speed (MH to M) on my Heil NTGM100 propane furnace. Am I going to "mess-up" something efficency wise, etc., by doing this? Thanks.
JR
1-check the "temp rise" across the heat exchanger,lower fan speed results in a higher temp rise, too high of a temp will kill your heat exchanger 2-check that the blower speed for AC is proper,some units are wired for only one speed for both heat and AC.Too low of a fan speed will ruin the compressor and your day !0 -
On the side of the furnace
Appears a temp rise,..Usually 40 to 80 Aprox. You have a heil or ICP unit and as long as you remain in the Temperature rise parameters, you are OK. Air flow becomes an issue of flow to furthest registers and if you are happy with what you get to the furthest runs..Go for it.
Mike T.0 -
OK. Just to be sure then- Temp rise is the difference between a reading at the closest(to furnace) heat register and return register. My Rating plate shows 40-70. OK?0 -
JR
Take the return air reading at the R/A duct just before it enters the furnace and the S/A about 1 to 2' above the heat exchanger.
Mike T.0