Zone Valve: Always wondered.....
adambuild
Member Posts: 422
Yesterday we had to replace an Erie zv and I was surprised how large the opening was inside the valve that the water flows through although not full port. The openings in the Honeywell zv's that we usually use are much smaller. I actually checked a Honeywell 1" zv yesterday out of curiosity and the opening inside was about 3/8"! Why so small? Is bigger better/faster response? What's the reason?
Thanks, Adam
Thanks, Adam
Most valves have a Cv listing
that indicates GPM flow. Some manufactures, Caleffi for one, offers zone valves in various Cv's.
If you use a zone valve for an indirect tank water heater always chose the one with the highest Cv rating.
hot rod
Hot Rod is correct as usual
The reason you may want a smaller Cv is for tighter control to a setpoint in a modulating control valve. This allows more proportional response to a change in the variable being controlled.
Imagine trying to control 0.50 GPM using a 1/2" reduced-port valve with a 1.2 Cv as opposed to controlling 0.50 GPM using a 3" butterfly valve..... you can see how a little movement on the 3" valve (with a higher Cv you bet!) means a lot more flow...
As Hot Rod said, with an indirect or other on-off/open-closed application, you want a larger Cv. You are not trying to modulate the flow but rather give it a huge "Yes" or a huge "No"."If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0 -
head loss
Yep, the Cv rating is very important. In many zone valves, a larger pipe size does not necessarily have a higher Cv rating.
head loss in feet = (1.52*gpm/Cv)^20 -
We askrd the Honeywell rep if
or when they would get a 1' with a higher cv ... they said they are definitely considerig it ..maybe Bill can tell us when these might be available for domestic hot water indirects.0 -
hydraulic force
i would think the reason for the smaller opening is to reduce the force against the valving mechanism, reduce valve slamming and wear? just a guess. psi x sq inches = force0 -
One of the problems with
a low CV rating with a High GPM pump is noise on shut down. It is there fore important to match the zone valve with the flow rate to insure quiet operaion.0