Pressure gauge question
Andy_14
Member Posts: 121
Attached picture shows system and gauges.
Do these pressure gauge readings sound ok? I thought shut down should only be around 12psi?
System shut down. Both supply and return gauges read ~20psi
System running, supply reads ~22psi
System running, return reads ~27psi
pressures
They seem OK to me. You will see higher pressures on the return gauge as you have two circulators adding head to the ssytem. If the pressure rises on the supply side, it can trip that safety valve, which should be piped down to the floor in case it does blow. Fine looking install otherwise.0 -
pressures
Looks OK>>>>you have two circs adding head in that side of the system. Nice looking install but pipe that safety to the floor. IF pressured builds on the supply side, it will blow and make a mess.0 -
Thanks Al. My biggest concern was the ~20psi readings while the system is shut down.
That is an old picture that was already on my computer. The PRV has been piped to the floor and a condensate loop has been added.0 -
This is the high point of the system apparently
It need not be higher than the minimum operating pressure of the boiler (enough to satsify the pressure switch). As Al was suggesting, give yourself a margin between your operating pressure and the relief valve setting.
Your readings of 20 static and 22-27 dynamic is your primary side pressure drop: 5 PSIG or about 11.5 feet of head. You may be able to plot your actual flow on the pump curve.
"If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0
- 50 Industry Classes
