Air Vent Sizing???
and they're not that difficult to add. Measure the length and diameter of your steam mains and we'll tell you what you need.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
  • Todd_26
    Todd_26 Member Posts: 2
    Air Vent Sizing ???
    My house was built in the late 1920s early 1930s and has a single pipe system with no air vents on the main line. I’ve been here 4 winters and have not done any maintenance (embarrassingly) during this time, other then drain and add water to the boiler.
    I had to replace a badly leaking air vent the other day. Following the chart in Home Depot I bought Maid O Mist sizes 4, 5, and 6 figuring that I’ll use them all at some point. When I got home I found that all of the radiators (11 in all) except 1 had size C and D air vents regardless of location to the boiler.
    My question is: since there is no main vent should the radiator vents be larger then the recommended size, or should I replace them all with the proper size for their distance from the boiler?
    Thanks for reading!
  • Todd_26
    Main size
    Steamhead
    There are two sections of the main that run in opposite direction from the boiler. Both are L shape, one is 25Ft with 5 radiators off it. The other is 30 Ft with 6 radiators. I'm guessing it's 2" pipe based on a 7.5" circumference. I will try to post some pics later.
    Thanks for answering.
    Todd
  • Steamhead (in transit)
    Steamhead (in transit) Member Posts: 6,688
    Yes, that's 2-inch pipe
    use two Gorton #1 or Hoffman #75 vents on each main. Let us know how much better it works.
  • Todd_25
    Todd_25 Member Posts: 1
    Air Vent Sizing
    Thanks for the info Steamhead. I'll try to do it next weekend and let you know how it home out.
    Todd