Boiler Temp

Uni R_3
Member Posts: 299
With 15psi, water boils @ 250°.
0
Comments
-
Boiler temperature
What is your professional opinions about what to set the temperature of a boiler? My original istaller set it at 220 degrees, which obviously was ridiculous and inefficient. Since then, I have moved it to 190 degrees, should, can I go lower and still heat the house efficiently? I have seen posts where people have said between 170-180, is this accurate? I am still fighting my original company about the poor installation, but it is getting fixed.
Thanks,
Phil0 -
It depends on the ratio
of radiation to heat loss. That determines your lowest maximum temperature on a design day. God help you if you need 220 degree water...
The upside of that is you will not complain day to day about too little heat; rather you will complain and loudly only one day of the month
If your heat loss is, say, 50,000 and you have about 335 SF of radiation or the equivalent if fin-tube, you should get by with 180 degree water (170 average assuming a 20 degree drop) as one example.
Do you know your heat loss and do you know your radiation potential? Those two together tell the story.0 -
boiler temp
180 is the norm not sure bout that 220 since water boils at 212 should have popped the relief valve0 -
As Brad W says above, it depends on the ratio of radiation to heat loss.
For instance, in my house I have finned baseboard. On design day (-4) according to the heat loss calculation I can get by with 150 degree water. It's actually -8 currently and I am running an average water temperature of 160 degrees. And some zones are cycling off. (The rooms on the west side of the house are about 1 degree below setpoint because they are dealing with the 20 mph winds , while the eastern rooms are getting all the prewarmed air moving through them and those zones are cycling off.)
You will need to do some experimenting to see how low you can go with the water temps in your particular system. Turn the temperature down in 10 degree increments and give it a couple days to see if it can keep the room temperatures up. You will need higher water temperatures when it is colder outside, and can use lower water temperatures on the warmer days during the rest of winter. Don't go so low that the return temperatures are below 140-150 degrees for an extended period of time. (brief dips when a zone first starts calling is ok) This can lead to condensation and boiler damage.
They do make outdoor reset controls that will change the boiler water temperature automatically as the outdoor temperature changes. The Tekmar 256 is the most basic contol. (others available for DHW / multiple stages / etc)
Michael0 -
Thank you all for your input, I have someone coming out next week about getting an outside temp. control that will fluctuate the boiler temp based on the temp outside. I'll play with it a few days and see how it works. Thanks alot0 -
A word of caution, Phil
Outdoor reset is a fantastic way to both increase comfort and to save energy at the same time. Be advised though, unless you have a Modulating Condensing (ModCon) boiler (meaning you have a cast iron conventional boiler), your reset options are limited.
Specifically, you have to protect your CI boiler from thermal shock and from flue gas condensation regardless of gas or oil. This means keeping the boiler return water temperature at least 135 degrees.
Ideally, I would want to see you decouple the radiation loop from the boiler loop. Keep the boiler between 140 degrees at the low end and whatever you need at the high end. The radiation loop can be separated from the boiler by a 4-way mixing valve or an injection setup, two of several ways to do it.
By doing so, your reset to the radiation can be deeper and proportional to the heat loss, enhancing comfort.
If you have a ModCon, forget what I just wrote.0 -
It didn't pop the relief valve, but it did solve the problem of the noise level I heard from the baseboard units. If sounded like Niagra Falls going around my house, as soon as we turned down the temp, the noises went away.0 -
At those high temperatures
and add to this if the circulator pumps toward the expansion tank (rather than away from it which is the correct way), cavitation could have been occurring.
High temperatures and low pressures promote what is essentially boiling which is not only noisy but damaging to your pump impeller...
Something for the list...0
This discussion has been closed.
Categories
- All Categories
- 87.1K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 58 Biomass
- 427 Carbon Monoxide Awareness
- 113 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 110 Geothermal
- 161 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 996 Plumbing
- 6.3K Radiant Heating
- 391 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 55 Water Quality
- 44 Industry Classes
- 48 Job Opportunities
- 18 Recall Announcements