Difficult Pressuretrol Adjustment
Mel_3
Member Posts: 15
Soon after my steam system was capped removing 3 of 10 radiators I noticed increased noise, in addition to short cycling (satisfying the pressuretrol well before the thermostat). The pressuretrol is a very simple Honeywell unit showing only the cut-in value, but not accurately. It is set by a screw-head on top. Inside there is a differential setting. I replaced the gauge with a 0-5 reading and saw that it was cutting out at 4 psi and cutting in at 2 psi. All radiators get warm, and after a while the thermostat is satisfied.
I adjusted it so that it now cuts out at 3 and cuts in at 1 psi. The noise level is way down-about how it was before. The short cycling may be improved a bit.
Here's the pressuretrol problem. If I try to lower the cut in any further, the adjustment screw (which is being turned counter-clockwise) comes off the part of the unit into which it screws and, of course, the pressuretrol ceases to function. Do I need a new pressuretrol? Does it make any sense to obtain a longer screw?
Thanks for your help.
Mel
I adjusted it so that it now cuts out at 3 and cuts in at 1 psi. The noise level is way down-about how it was before. The short cycling may be improved a bit.
Here's the pressuretrol problem. If I try to lower the cut in any further, the adjustment screw (which is being turned counter-clockwise) comes off the part of the unit into which it screws and, of course, the pressuretrol ceases to function. Do I need a new pressuretrol? Does it make any sense to obtain a longer screw?
Thanks for your help.
Mel
0
Comments
-
.
that pressuretrol is not suited to residential heating -nor commercial heating -in fact the pa-series -pressuretrol that comes with every new steam boiler shoild be tossed --they are not sensitive enough and the range is too high ------you will have issues since you reduced your load --get a pro in there to see what can be done to make the "system" work as good as it was meant to---------oh yeah a longer screw will not work --( i have tried)0
This discussion has been closed.
Categories
- All Categories
- 85.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 424 Carbon Monoxide Awareness
- 72 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 129 Geothermal
- 160 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 878 Plumbing
- 5.9K Radiant Heating
- 375 Solar
- 14.6K Strictly Steam
- 3.2K Thermostats and Controls
- 58 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements