MCF Nat gas and BTU
Jim Bergmann_2
Member Posts: 79
Was at CSA lab, and saw the heat content of gaas varies form 930 to 1050 over the course of an hour sometimes, 1025 seems to be a good average
An MCF = 1000 CF
Average BTU Content of Fuels
Fuel Oil (No. 2)140,000 BTU/gallon
Electricity 3,412 BTU/kWh
Natural Gas 1,025 BTU/cubic foot
Propane 91,330 BTU/gallon 2500 BTU/cubic foot
Wood (air dried)*20,000,000 BTU/cord or 8,000 BTU/pound
Pellets (for pellet stoves; premium) 16,500,000 BTU/ton
Kerosene 135,000 BTU/gallon
Coal 28,000,000 BTU/ton
From U.S. Department of Energy
An MCF = 1000 CF
Conversion of MCF to BTUs
NEVER MIND GUYS!!! SHOULD HAVE GOOGLED IT IN THE FIRST PLACE!!!
I know that 1KW will produce 3415 Btus. What about 1MCF of natural gas to Btu and also oil to Btus?
Thanks,
Rob0 -
It depends...
Natural gas has a range of BTU contents depending on what the admixtures are. Natural gas is mostly methane (CH4; about 94-97%) and the rest is made up with butane, ethane, propane and other 'anes... plus air, CO2, fossilized dinosaur flatulence...
The BTU content varies with local supply; the gas company may have a deal on butane or propane they can mix in at the distribution point. (Is it still "natural" at that point? Mmmmm....)
Methane itself is about 1,000 BTU's per CF which sets the standard but as "natural" gas can range up or down 50 or more BTU's per CF. In the end you are charged for "therms" or 100,000 BTU blocks, so if they add more ingredients which raise the BTU per CF level, don't worry! You will be charged for them in full...
In short though, 1,000 BTU's per CF is a good figure.
Fuel oil: #2 is traditionally given as 140,000 BTU's per gallon total heat content. This too can vary by a couple of thousand depending on source of supply, degree of solids, etc. 138,500 BTU's per gallon is a conservative number I have in my Mark's Handbook. 138-140,000 would be fair figures.
The higher grades (less refined) such as #4 and #6 have higher fuel contents, over 150,000 due to having more "chunks"
Not that you will be burning the stuff, just for comparison.0
- 120 Geothermal
