Radiant heat how far can a 1/2 loop of pex be run.
Options

Weezbo
Member Posts: 6,231
they are about 150 feet long one way with a companion hose that is taped to it for a + and _ S&R ...they have a no kink boiler purge sweat on to a Wee..irsbo 3/4cuX1/2 pex adaptor/coupling.
i use these as run outs to headers when dialing in the remote headers ,or to what we call Unit heaters, a fan + coil...feed 2000SQ '+ slabs as i roll. i have larger ones in 3/4" and larger ones in 1"
today i was considering making up some in 1 1/2" to a 2 1/2" headder with camlock....
dont freak on short loops....other than make sure you dial the temps down as low as you can get them...
i have had over 108 degree delta t on them with supply side under 128F....*~/:)........Recently :)
i use these as run outs to headers when dialing in the remote headers ,or to what we call Unit heaters, a fan + coil...feed 2000SQ '+ slabs as i roll. i have larger ones in 3/4" and larger ones in 1"
today i was considering making up some in 1 1/2" to a 2 1/2" headder with camlock....
dont freak on short loops....other than make sure you dial the temps down as low as you can get them...
i have had over 108 degree delta t on them with supply side under 128F....*~/:)........Recently :)
0
Comments
-
radiant floor heat
How far can a loop of 1/2 pex be run from the boiler and back. We are looking at 120 feet to and fro from the boiler and a room size of 350 sq ft.0 -
120 feet does not scare me
Depending on the manufacturer and ID tolerances and flow rate, 250 maybe even 300 feet would be possible. Your 120 feet per circuit should be fine.
Remember though, it is not the pressure drop and flow characteristics alone, but the coverage/density and overall temperature drop. Keep the Delta-T's low (10 degrees or less) to obtain the most even floor temperatures.
I have no idea what your heat loss is or your floor mass, but at first glance your 120 LF assuming it is the entire circuit, seems "thin" when applied over 350 SF of room. That is about one foot of tubing to 3 SF of floor. Even 12" spacing will use up 350 LF of tube. Hope you are running multiple circuits.
Have you checked out everything?0 -
brad, I think he's talking about doing one loop for a room, that is 120' away from the mech room round trip.
Personally, I no longer buy the 10 degree dT design philosophy. we do it to raise average loop temps in some cases, but I've adopted a 20 dT design philosophy and have had no reports of noticeable floor temperature variation as of yet. 10 dT is just a lot more flow than you really need in most cases.
Funny thing is at a 20 dT, if your loads are low you can run 500-600 foot loops in some cases.
But it all depends on load. heat load determines flow rate. Higher loads, more flow, shorter loops.
If the original poster wants to ballpark this, I'd do it in two loops.0 -
tube length
I read it differently?
Is there 60ft between the boiler and the 350sf room to be heated?
Sounds like time for a manifold in a closet or crawlspace w/ 3/4" S&R from the boiler and 3 loops of 1/2" at approx 200ft each at 8"-9" on center if this is living space.0 -
layout
Rob, for slabs, do you lay the loops out in spirals generally in order to keep the floor as uniform as possible?
Generally what I have done is embedding loops within each other and supplying them from opposide ends.
I think constant circulation helps even out the floor temperature more than anything.
Just curious.
0 -
Nope, basic serpentine only, in most cases. We do use PWM thermostats and reset control and/or Indoor feedback on pretty much all of our systems though, so operation is pretty consistent, if not truly constant.0 -
NRT Bob
Thanks for clearing that up, Bob- I had not seen it that way obviously. I wonder what it really is.
I suppose a 20 degree drop (half the flow, oh joy) can work but I think best when in a thick slab deeply set. How does that work in thinner slabs and Climate-Panel type systems? I seem to get striping when I try to drop the flow rate. Just enough to notice.
Thanks for keeping me straight!
Brad0 -
Climate panel *requires* designing around a 20 degree dT, last I knew.. at least, all the 'quik trak' design info is based on a 20 degree dT.. 5/16" pipe can't handle much higher flow rates. That's what made me start wondering... if it works for that, why am I designing around 10 for everything else?
If you're getting *striping*, your water temps are too high and the system isn't running long enough on cycles. If you notice temperature changes from one end of a loop to another... not sure what to say, I've never had any feedback from anyone noticing that. Maybe if you really tried you could, but most people aren't really trying, and if they don't notice, I'm not going to bring it up
Pushing a 90 kBTU load with on 3-speed brute is pretty sweet though0 -
The Circulator Doesn't Know ...
where its going to live.
If you didnt have anything else to do today, and you have, say, an Uponor/Wirsbo CDAM, you could draw a system curve on top of a set of pump curves for, say, a 15-58, for, say, a single 300 loop of 1/2 pex. Thats the only way to predict what youre going to get through that tube. You may want to add a couple of feet of head for supply and return losses.
You can design for flow rate per tube or for ∆T, but dont forget that the circulator is most likely on a shelf, in a box, in the dark, does not know that we are having this conversation, and will do whatever it wants when you fire it up, no matter what our plans are.
0 -
George, I don't see the value of this comment. Are you suggesting that running the numbers isn't useful?
Obviously you have to calculate flow and frictional loss to size a pump. If you don't, you're guessing.
I'm not saying you're going to nail a ten or twenty degree dT in the field exactly because that's what you designed for, but it certainly tells you what kind of flow rate you need, how to balance, how long your loops can be, how big of a pump you need, how big of a pipe you need.
right? or are you just guessing at all of that too?
So it's not like design dT doesn't matter. You can ignore it and design around "rules of thumb" if you like, I suppose. Me, I'll push 75kBTU loads on a UP15-58 pump because I know how much flow the system NEEDS, I know the frictional losses in that system), and I know that the pump will do the job (because I looked at the pump curve). My system will use smaller pumps, smaller pipes, less electricity, and less loops. And the numbers will be close enough. OR, I'll know that I just can't do that on this particular job because, say, someone already installed a 350' loop in a high load area!
THAT'S the value of running the numbers, not that every factor is correct to the second decimal point in the field, but that I can approximate with great enough accuracy to make better design decisions than if I don't do the numbers.
It also tells me fun stuff, like whether this room would ever heat with a 350 foot loop or whether you'd have to eat holes in the pipe to push all the flow a room needs to keep the back end of the loop from being stone cold when you're under a load. And when you run the numbers, you realize that some rooms could handle 500 foot loops and some you really shouldn't push past 250.
I don't really care what the pump thinks, pumps are dumb... that's why I pick the pump I want and I set up the system, not the pump.0 -
Jack: Must agree with NRTrob that you'll need at least two runs for that 350 sq.ft. room with 60' (120' round trip) from the boiler if using 1/2" tube. Three or even more runs required depending on load per sq. ft. of floor area.
NRTrob: What do you consider to be a "low" load?
0 -
Nice Try Mike
Let's say, though, that he's got a 1000 BTU load on this room. That's only .2 GPM with a ten degree drop... very acceptable. his frictional loss would be about ONE foot of head in that case, pushing .2 GPM through 470 feet of 1/2" pex, roughly. Very doable. the water may not actually come back exactly ten degrees cooler than it goes out, but you know the pump can do this.
If he's got a 5000 BTU load, 1 GPM.. or .5, if he can handle a 20 degree drop, which might mean his supply temp has to go up a few degrees.. and at .5 GPM, that 470 foot loop is still only 5 feet of head.. a standard UP15-58 would push up to 13 GPM if that were the maximum head it were facing. Even if it's not dedicated to that loop, if he can balance, you're still not upsizing your system pump and this is totally doable.
But if he's got 20 BTUs/sq ft, for a 370 sq ft room, that's 7400 BTUs.. .75 GPM even at a 20 degree drop.. now he's up to 12 feet of head. That UP15-58 could still do that on low speed, if it's dedicated, but just barely. If he's got a system pump though, now that high speed 15-58 can only push 6 or 7 GPM through a balanced system. Probably time to upsize.
but it goes up fast after that. Since I have no idea what his load is, I would split into two to be safe if I had to do this blind.
0 -
Rob, I didn't write right
... no offense intended. The "pump in the dark" comment was as you said. Pumps are dumb. And I would love to draw a system curve for a single loop (and 2, 3, 4 ...) over a 15-58 set of curves, if only i could figure out how to post it. Wondering out loud ... maybe could do it in Excel, save it as a pdf ... grunt ... oof ... save that as a jpeg. Or hand draw it and stick it in the mail.
I forgot to mention that for 1/2", I design for 0.9 gpm per pex loop, to keep the velocity close to 2 fps, then calculate the delta T. I like it less than 10°F. so I don't have to be concerned as much with layout patterns.0 -
well, no offense intended here either george, but you're designing for at least double the flow rate most loops need, even at a 10 degree drop, and no one would ever be able to tell the difference if you ran the flow slower, except during the initial cost of the system and the electrical bills.
I suppose if you're doing fixed temp, bang bang strategies this may be more of a concern. But if you're using reset, and assuring more consistent heating cycles, you really don't need that much flow the vast majority of the time. the loop will heat evenly. But then, none of us are doing bang-bang systems anymore, right?
Frankly, I've seen a lot of charts talking about laminar flow kicking it at around less than 2 FPS which is supposed to cripple our heat output, or talking about air coming out of solution at lower flow rates, and the vast majority of us out here are running around .5 GPM per loop... here, we're routinely running .2 GPM as an arbitrary minimum... with zero problems. So something's up that the charts are not reflecting... we do occasionally get a bubble in radiators or a baseboard, I think it does finally cross a line there, but in 1/2" PEX I'm just not seeing it.0 -
OK, I'm coming around ...
... it's about power consumption. Yesterday, while riding with a wholesaler's outside salesman on some contractor calls, I told him that the day was not far off that straight circulator zoning would be an energy code violation. I told him about a 10,000+ sf house that had over 24 zones, a 007 on each one. On a design day, that's 1.5 kw just to move water around.
So, from now on:
1)If I'm able to influence the choice of circulator or actuator zoning, I'm going to bring up the subject of power consumption.
2)At that 0.9 gpm per circuit flow rate, some of the calculated delta Ts are only 2 or 3 degrees. I pledge to seek a happy medium.
3)I will await the universal availability of really low wattage circulators like the Grundfos 15-10.
Keep the woodbox filled,
George0 -
At least one...
Manufacturer suggests 250' of 1/2 PEX is the physical limit for any one length.
It is merely a guide, not a substitute for doing the math.
I think that's all the questioner wanted to know.0 -
300 foot
is the RPA suggested max length. This works nicely as most manufactures sell 300 and 600 foot coils in the barrier pex.
I will sometimes push 333 footers when I buy the 1000 foot coils.
If in fact you need to run 120 feet to and from be sure to insulate that sectiuon even if it runs through heated space.
If the design calls for 12" on center for your job, that would require a 350 foot lop. A tad long for my taste, considering the long leader length to be added.
I'd use 2- 200 foot loops, manifold them and supply the manifold with 1/2" insulated, supply and returns.
You might tighten the spacing on the outside walls to. If that is the case use a pair of 300 footers. No cutting or waste required
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 87K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 115 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 107 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 983 Plumbing
- 6.3K Radiant Heating
- 389 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 48 Job Opportunities
- 18 Recall Announcements