Perry's new installation - Vitoden 200, 6-24 & DHW
GW
GW Member Posts: 5,137
just kidding, that's sems like a great idea; just like a ci rad, it will capture the bubbles and let it rise to the top of the llh.
where is the pic?
going back to bed, I woke up to deal with my ailing Treo 650 phone; i filled the memory so much it wouldn't start up. Made me pretty nevrous!
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=368&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
Gary Wilson
Wilson Services, Inc
Northampton, MA
gary@wilsonph.com
  • Perry_2
    Perry_2 Member Posts: 380
    OK, I know you all want to see how it turned out.
    I built the wall (with the boards) at this time just for this project - and used 2x6's where the Vitoden would go.
    The grey box on the right side of the boiler is a Brickwall industrial surge protector (good for up to 20 amps - and capable of absorbing thousands of surges without degrading as the cheaper surge protectors do - this is close to a $300 surge protector).
    I will wire in the LWCO when I get it to this box (could not get the Vitodens LWCO fitting for the top of the boiler in time). Note that there is no requirment for me to use a LWCO; but I will install one when I get the right adapter.
    The surge protector only powers the boiler recepticle under the power supply.
    Items that may be of interest - or debate:
    Yes, those are secondary loop supply and return thermometers (in thermowells).
    The TACO 007 Circulator is on the return side of the Low Loss Header (the silver thing in connecting the boiler and the secondary loop - you are really looking at the insulation kit). Please no discussion on pump location - I understand the theory and debate. The installation contractor believes this is the best method - and I never had any air problems with the old boiler with the pump on the return side. Given the low head of a TACO 007 I don't see a problem.
    The circulator is installed with the motor against the wall. The contractor feels that it is best to change the entire pump for a few dollars more than to just replace the cartridge.
    There is a system isolation valve after the air scoop (not easily seen in the pictures). I don't want to have to drain the entire system if I have to work on it. The Circulator has isolation valves as part of the flanges.
    There are low point drains and a vent valve for the DHW supply line high point. I believe in making maintenance easy...
    There are female copper fittings threaded on the low loss header. The installation contractor is aware that there is debate on that - but has never had a female copper threaded on black iron joint leak in over 20 years of installing them - and views installation of a coupling as adding another joint that could leak.
    Not easily seen - but there is a switch to turn off power to the boiler recepticle (right next to the recepticle). Oh, I tend to wire with BX cable. I may be crazy... but it is a better kind of crazyness than things other people do.
    Anyway, I hope you like the pictures. I plan on shortning up the cord to the power supply some day.
    I should also make mention of the good work from the following:
    LeClaire Brothers Heating, Two Rivers, WI
    Gary Jansen (Mfr Rep). Fluid Handling, Milwaukee, WI
    The system is up and running well now that the miswire cable plug was found and corrected (another thread has that discussion. It took the rep 6 hours to diagnose it - but we sure learned how to take apart and test all kinds of things in the boiler in the process).
    How much will this all cost.... Don't know yet. The job was based on T&M format as the contractor had no experience with this type of boiler and vent system. Those extra 6 hours that LeClaire had their crew here for diagnostics by the rep (OT) are my responsibility. We've been talking about those hours... We'll see.
    Have a great day.
    Perry
  • ALH_4
    ALH_4 Member Posts: 1,790
    Looks great
    The installation looks great.
    With that pump location, the system head loss will be added to the boiler pressure, but like you say with a low head pump like a 007 that is probably only 4psi. Ideally the system pump pulls on the LLH and the expansion tank plumbs into the bottom of the LLH.
    It's always nice having thermometers in the system if you're trying to figure out what it's doing. Throw in a rotometer and you'd know exactly what's going on at any point in time.
    -Andrew
  • Steve Ebels_3
    Steve Ebels_3 Member Posts: 1,291
    PONPC for general discussion
    When we install a Vito with a LLH I put a tee in the bottom tapping of the LLH and run a line to where ever we hang the XP tank. This makes the LLH the common PONPC of the whole system whereby all circs are pumping away from it including the boielr circ. We just fired one up Thursday (6-24) driving 320 sq ft of Climate panel, 9 panel rads and 2 towel warmers. Done this with the last few installs and have been very happy with the results. I haven't incorporated any air elimination device into the last few other than the vent on top of the Vito. We just purge the blazes out of the system and let er rip. No air problems at all. Period.
    If you look at Viessmann's installation drawings, that's not the location they recommend. Anyone see a long term problem with my method?
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928
    Enjoy yourself Perry!
  • ScottMP
    ScottMP Member Posts: 5,882
    Just curious
    How often do you empty the drain under the sink :)
    What do you have for heat emmiters in the house ? I notice no purge station ? Interesting to put the feed near the expansion tank and not pump away ? Why go half way ?
    Scott
  • Perry_2
    The plastic jug under the sink...
    That plastic jug under the sink does not fill up; and only deflects the sink drain into the floor drain.
    It's on my list of future small projects- but here is the situation.
    The floor drain is in a square 4" deep floor basin. When I put beadbord on the basement walls, studded them, put the boards on, and changed the way the sink is plumbed to hose connections in the back (instead of hard piped from the side) - I endid up moving the sink out about 8" from where it used to be. The result is that the old sink drain no longer lines up to the center of the floor drain basin - and in fact would dump directly on the floor. That would make quite the mess during laundry as the wash machine drains to the sink.
    I cut a hole in the side of the gallon jug, popped it on the sink drain and propped it up with a 2 x 4. Works great. Water now runs (or bounces) into the floor drain basin. I added a splash plate on the wall.
    Someday I will modify the sink drain so that it again lines up with the center of the floor drain basin. Until then - the jug diverter system works well.
    As for your other questions - see my original post on this thread.
    Perry
  • Perry_2
    Emmiters and purge..
    I have cast iron baseboard on a Monoflo T system.
    There are two purge locations built into the boiler by Viessmann.
    A top of the boiler purge connection, a bottom of the boiler purge connection. Viessmann supplies a plastic hose that can be connected to the boiler purge locations.
    Hope that helps.
    Perry
  • Ted_9
    Ted_9 Member Posts: 1,718
    system purge
    I would have put a system purge since technically that one on the boiler is a boiler drain, but it may be fine since each radiator has a vent. Do they?
  • Ted_9
    supply
    One reason I always pump away is that you dont know who will be there next. Owner sells the house or puts in an addition. The next guy adds a circ where the existing one is. Then the breeze way gets enclosed and they want heat in there. That guy connects to the return as well. On and On it goes, then you see stuff like this:
  • Constantin
    Constantin Member Posts: 3,796
    Looks good... and some suggestions
    I'd consider insulating the piping, especically the piping to/from the Vitocell. Otherwise, that'll leak lots of heat out of the tank. The heating piping may be worth insulating as well, depending on how you plan on heating the basement space.
    I like your prescience on installing a hefty surge-surpressor. I went a step further and installed a UPS for the Vitodens install I am peripherally involved in. It allows the whole heating system to run for about 6 minutes (3 pumps, the Vitodens, and the control tidbits), which is much longer than it takes the generator to start.
    Plus, the UPS conditions the power, which is a huge problem in the area that this Vitodens is installed in... line voltages fluctuate like a Yo-Yo! The generator output is less than even also... and the UPS is designed to clean up that kind of power also.
  • Paul Pollets
    Paul Pollets Member Posts: 3,671
    Suggestions
    The airscoop fitting requires 16" min length on the inlet side from the last fitting to allow laminar flow. Shorter distances mean less effective air removal. I'd be using a Spirovent, which doesn't have min inlet requirements. The expansion tank is supposed to be located on the boiler supply, before the LLH. We also use circ isolator flanges and ball valve on the return with a purge, to help isolate all components and make it easy to service... Same with the DHW tank...we isolate all ports and provide ball valves. And as Connie said, insulate the piping.
  • Weezbo
    Weezbo Member Posts: 6,231
    you have something worth doing right stashed in the place
    nice choice:)
    the pointers you have from everyone do tend to reduce minor technicalities so dont dissmiss them as nit picking...the low loss header was a good way to go.
  • Ernie
    Ernie Member Posts: 94
    Constantin
    May I ask what type generator set you installed, NG, LP,Gasoline, or diesel and what kind of output? This is mine but is in WIP stage. Hope to have it finished in about 2week if Asco Technologies can send me a correctly manufactured Transfer Switch. I am frustrated but patient, things happen.
  • Constantin
    Hi Ernie,
    The genset has been there for a couple of years and is a 10kW Dayton-branded unit that runs on LP. If memory serves correctly, it's a small FIAT engine in there!
    It runs the fridge, some lights, and the heating system.
  • Perry_2
    Radiator vents and system purges
    Yes, each radiator has a vent.
    I am not sure what you are looking for as a system purge; but both the boiler supply and return piping have low point drain valves.
    Another item not shown is that their are 3/4" valved connections that branch off the new copper to allow for future additional basement heating - if it needs any. Since I beadboarded the basement I had only turned on the old heater once. There is about 100 ft of 1.25 inch pipe, plus a lot of smaller feeder pipe that makes a good emmiter for heating the basement.
    Perry
  • Perry_2
    UPS issues with LWCO's
    I had also considered a UPS - and was looking at one that would run the boiler for a hour or two if needed.
    One of the issues though is that if the UPS is hooked up by just plugging it into the recepticle - and the boiler into the UPS -- that the UPS will defeat a LWCO that cuts power to the recepticle.
    I am aware that you could go out of the normal way and wire the LWCO after the UPS.
    Maybe I'll do something like that in the future.
    Just something to consider.
    Perry
    Perry
  • Perry_2
    Thanks for the suggestions.
    Please keep them coming.
    I know that this is not a perfect install. Those of you who have followed my journey know the difficutlty I had in finding a vendor to do the install. Some things were changed from what the vendor would have done. But, I have learned to pick my battles - and not try to fight them all.
    I had already thought of insulating the hot water heater circuit pipe (at least back a ways). I use the radiation from the basement pipe as my basement heating system - so I won't be insulating the other pipe. I do note that there are provisional 3/4" valved off stubs on the supply and return should someone want to add more basement heat in the future (although I think the beadboarding of the basement has done wonders).
    If there are future maintenance invovling the pipes I will see what I can do to adopt changes at the time. Otherwise, as long as it works - and I don't have air problems - I'll leave it be for now. It will be a while to pay this off.
    Now I need to get it tuned to my house.
    Have a great weekend. I'm on 12 hour days for most of the next month or so.
    Perry
  • Uni R_2
    Uni R_2 Member Posts: 589
    LWCO
    Perry, is the LWCO a Viessmann product? Can you show a picture of it when you get it installed on the Vito?
    Do any others use LWCOs of Vitodens boilers when not required by code?
    You must be very pleased. How long did it take to learn the controls? ;-)
  • GW
    pics
    pics are like blood in the water here, eveyone flocks to a boiler install picture
    Nice job!
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
  • Perry_2
    Update
    The LWCO adapter (it screws in) is a Viessmann product. You are then free to use whatever LWCO you want. Viessmann does sell a "rebranded" LWCO if you want to buy it.
    My heating contractor has indicated that the adapter and LWCO is in - awaiting my return to normal work hours so that it can be installed.
    Concerning using the controls. It took several days to learn what house temperature setting was OK on the RS control unit. Since then, all I have done is watch. Rock steady house temperatures, and the Vitodens has cycled on and off and changed circulation temperature as needed (circ temperature ranges from about 85 F to 115 F so far). I did note (by comparing the circulation temp to the outdoor temp) that the Vitodens has learned that it needs to be on Reset Curve 1.0 for those of you who understand the different options - at least for the fall weather we have been having (the rep had set it at I believe 1.4). This thing self learns (the advantage of adding the RS control unit).
    I have yet to play with the night setback - or even set the clock on the Vitodens (It thinks it is in Germany). I've been far to busy at work.
    In another week I should be done with the power plant outage and have a more normal schedule. Time to learn the controls and play with the nightime setback at that time.
    Perry