Joe_76
Member Posts: 34
Why is there such a discrepancy between BTU values per SQUFT for staple up with a reflective barrier. Each manufacturer uses a different value ranging from 15BTU to the Ipex program which I use that has a maximum of around 20 BTU SQUFT. Some figures even state more than 25BTU.
Thanks
Joe
Thanks
Joe
0
Comments
-
I've seen claims as high as 50 btu/sq. ft!
One rule of thumb is 2 btu for ever degree difference between the radiant surface temperature and the room air temperature.
82 is about as warm as you would want the floor surface in a residence. Use an air temperature of 68.
So 82- 68=14 time 2 btu/ sq foot comes out to 28btu/square foot. That seems to be a realistic number most will agree on for a comfortable radiant floor design.
If you want more output either raise the floor temperature or maintain a lower room temperature. We do both on some large truck shops. Workers can be comfortable in a 65 degree space under moderate to heavy work. And floor temperatures can be a bit hotter if they are not standing bare footed.
85 floor temperature with 65 air would give you a 40 btu/ ft output.
I wouldn't count on that in a home. First you will have sweaty feet, and 65 air temperature will seem a bit chilly. I've found senior citizens like 72 air temperature, radiant or not.
If you have a radiant desitgn software program you can run these "what if" scenairos
Reflective insulation is a bit questionable from my experience. Rare to see it stay shinny and reflective, so that claim is questionable.
Real hard to beat a conductive transfer afforded by transfer plates and a good r-value below. Save the reflective surfaces for your bathroom mirrors
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements