sizing charts for cast radiators BTU values
Options
Mike T., Swampeast MO
Posts: 6,928
See this book:
<A href=http://www.heatinghelp.com/shopcart/product.cfm?category=2-59>EDR by Dan Holohan</A> Some sample pages are available for viewing and you can always buy...
Note that radiators are rated by EDR (equivalence of direct radition) NOT output! EDR allows comparison among rads of different design/manufacturer.
For output in a hot water system you MUST know the average water temperature available to the radiator.
If you're making modifications to an existing system, ASSUME NOTHING! To avoid nightmarish balance problems that require extensive and expensive piping/control changes to correct you MUST assess the current system. You need a room-by-room heat loss calculation. Then estimate the average radiator temp required in each space to meet this loss. Then size any new or modified radiator similarly.
A <I>very</I> common mistake/problem reported here is sizing new radiation in old hot water systems using the "standard" output at 180° average water temperature. In many cases the average water temperature in the existing radiation will never approach this level and your new radiation will be terribly undersized.
<A href=http://www.heatinghelp.com/shopcart/product.cfm?category=2-59>EDR by Dan Holohan</A> Some sample pages are available for viewing and you can always buy...
Note that radiators are rated by EDR (equivalence of direct radition) NOT output! EDR allows comparison among rads of different design/manufacturer.
For output in a hot water system you MUST know the average water temperature available to the radiator.
If you're making modifications to an existing system, ASSUME NOTHING! To avoid nightmarish balance problems that require extensive and expensive piping/control changes to correct you MUST assess the current system. You need a room-by-room heat loss calculation. Then estimate the average radiator temp required in each space to meet this loss. Then size any new or modified radiator similarly.
A <I>very</I> common mistake/problem reported here is sizing new radiation in old hot water systems using the "standard" output at 180° average water temperature. In many cases the average water temperature in the existing radiation will never approach this level and your new radiation will be terribly undersized.
0
Comments
-
Where?
I am looking for a refference chart which gives btu values for any given Cast Radiator size. They are all Hot water. Any help would be greatly appreciated.0
This discussion has been closed.
Categories
- All Categories
- 87.8K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 133 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements