Cellulose Insul gave me 20% savings from last year
If you only got a 20% savings then I would suspect a large portion of your heat loss was from things other than where you insulated such as doors, windows, infiltration and still uninsulated parts of the envelope. ......or the filling of wall cavities wasn't done properly.
Looking at the house on a cold day with a thermal camera might tell you a lot.
Also comparing heat usage at 53 degrees can be very inaccurate since variable amount of heat from cooking, lights and indoor activities is a major portion of your heat during the shoulder seasons.
Ron
  • D107
    D107 Posts: 1,950
    Savings Calc Methodology Questions for 1924 house
    Been waiting for the latest gas bill. Luckily the average temp was the same 53 degrees for both periods mid Oct to mid Nov. I took the following efficiency measures:
    1. In March I had cellulose blown in to the 4" between sheathing and walls.
    2. End of Nov '05 I had the fireplace flue capped. (So savings from that was realized for only half the period.)
    3. This heating season I lowered the supply temp to 160 from 180.
    4. Did about 20ft of caulk sealing in attached sunroom on slab. Some basement bandjoists filled with fiberglass.
    In this period I used 64 therms (2.21 a day) compared to 80 therms, (2.76 a day). Thermostat settings are weekdays 65 6am-8am and 7-10pm; weekends 65 7am-10pm. Setback temp for other times is 62 this year and 60 last year. (very little effect since it was so warm night heat rarely came on.)
    This is a 210K gas-fired WM atmospheric installed 1982 (165DOE and 143Net) with a 40K loss and 80K gain, 2 floors cast iron and basement Slantfin 15.
    I think I may also have saved an additional 5% or more between 2004-05 by removing 4 complete wooden rad covers and 2 partial metal covers (top only 'trays').
    My question is, if the comparative temps were not the same, how would I calc in the average monthly temp differential. Or is the average daily temp for the period a true basis for savings calcs? Better to use degree days?
    Thanks,
    David
  • jp_2
    jp_2 Posts: 1,935
    heating degree days
    thats your best bet.
    but you've changed about all the variables, so it'd be tough to pin point what-saved-what.
    off hand I would hope that insulating a non insulated house would save more than 20%, could still be drafty.
    did you insulate attic too?
  • D107
    D107 Posts: 1,950
    Some more main steps
    1. Adding 3/4" tongue in groove styrofoam under new vinyl siding. That's next month. Should also better weatherseal doors. Windows are vinyl replacement double-pane from 20 yrs ago, still in pretty good shape. Someday insulate spaces where old metal weights hung.
    2. Put polyicinine foam under attic eaves and on gable walls. I'm going with a non-vented attic. (Westchester, NY).
    3. Remove direct hwh and install direct to existing boiler. hoepfully next month.
    4. Someday when I can do major piping job to correct series piping rad to rad, I'll also add a mod/con boiler, re-insulate basement.
    I'm happy with 25% savings from all I mentioned but I guess your experience tells you it could be more. With the 3/4 styrofoam and all the other things I'm guessing it could go to 50-60%.
    Things had to be done when they had to be done so yeah tough to isolate each factor. But hereon in I should be able to get a read on the styrofoam, indirect, then the attic insulation, the last one separately.
    Whether I go by avg. outside temp or degree days, how do you calc vs usage? If there are 100 degree days one month from 06 and 200 same period in 05 and your therms are X (or outside temp is 50 one month and 40 the next) what's the formula? Just divide degree days (or avg temp) by therms or vice versa?
    Also my electric went down 12% for that month. Since my gas bills have been over $2200 a year, savings is welcome.
    Thanks,
    David
  • jp_2
    jp_2 Posts: 1,935
    quick point
    when you redo your siding, why don't you remove existing window trim and foam seal the window openings(old window weight area)?
    then add the 3/4 foam board and foam the gap between window and 3/4 foam board.
    time to go or I'd explain more
  • I agree with JP
    that degree days are the best indicator. Are the savings you cite in dollars or therms? Therms are the only real benchmark as you can imagine. Bottom line number for conversation is "Therms per Degree Day" so it will be comparable year to year.
  • D107
    D107 Posts: 1,950
    savings are in therms
    thanks Brad. Sounds like you have to keep a daily record of use then? And then I'd have to find a nearby weather station (probably White Plains, NY) to get those stats.
    Not sure how diligent I can be about daily counts. No ballpark formulas for monthly avg temp?
    David
  • Our gas bill shows the total degree-days for the billing period (usually one month). We divide the therms shown on the bill by the degree-days shown on the bill. Actually we use the average July/August monthly consumption as a baseline (usage due to hot water, drying, cooking etc) and subtract that from the monthly winter therms.
    If your bill doesn't have degree-day information, wunderground.com has a 'History' function. Our gas company also shows degree-days in a web table, updated daily.
    Of course, in all cases these ddays are for a major airport in the area rather than specifically for your house.
  • D107
    D107 Posts: 1,950
    Thanks, that's a good site,
    and I've contacted them re: how to find degree days for specific time intervals. Yes the july/august is a good base for non-heating usage. I add a little to account for slightly higher winter HW standby losses due to lower house temps. But the non-heating usage --contrary to the utility's pie chart-- seems to be only about 15% of total. If we had kids and cooked alot I'm sure it could easily be 25% plus.
    What area are you in and what utility? I use Con Ed.
    Thanks,
    David
  • Summer DHW Usage
    I would not skew your summer numbers for winter use, David. The "dirty little secret" about DHW standby losses is that they are greater in summer.
    Sure there is less delta-T and the ground water is presumably warmer (this swings a bit across the seasons anyway). The average ground water temperature below frostline is about the mean temperature of your climate anyway. It cancels out overall. In late fall the ground temperature peaks, in early spring it is as cold as it gets.
    But consider that in summer you do not want additional heat, it works against comfort and any AC you have going on, for what that is worth. And in winter, any losses go to heat your house.
    Stick to the big picture of degree days and subtract your summer usage as a net.
    My $0.02
    Brad
  • D107
    D107 Posts: 1,950
    insulating the side of window cavities can be more easily done
    when we get to repainting/finishing the inside--yet another big project. (Not doable from the outside, yes? Contractor will be bringing out windows an inch or so to make it even with vinyl.) I've seen the online video on this old house. it's not that difficult--have to carefully pry the two side window moldings off.
    Actually even with the blown in cellulose, infra red photos showed how much the non-staggered 2x4 studs and window headers were conducting cold into the house; not much we can do about that.
    (Of course my wife's eyes glaze over when I start talking about any of this efficiency stuff. Thank God for the Raccoon Lodge, --er.. I mean The Wall. She is far more concerned about the nightmarish psychedelic mushroom-inspired 1960s kitchen wallpaper we inherited from the prior owners.)
    Thanks,
    David
  • What is your attic insulation? Cellulose is great there.
    Ron
  • Bingo-
    You nailed it Ron. Excellent points and posts from the best of sources.
  • D107
    D107 Posts: 1,950
    infra red photos
    Thanks for all the feedback. These infra-reds (b&w and color versions) were not done at optimum time. March 30, probably 40 degrees around 10AM but they give some idea. I watched the cellulose workers and though I'm not trained in this they seemed to stuff those cavities to bursting. I also made sure they opened additional clapboards in areas where firestops prevented full access.
    Attic: currently there's some old fiberglass under attic floor, probably 4", but it's compromised in areas and some of the covering floorboards are out of place. AC handler is up there and ducts penetrate floor. We have some work to do in that regard. I notice that on cool not cold mornings, the 2nd floor --underneath attic-- will call for heat when the main floor doesn't so I'm sure we have a chimney effect going on from some (partially insulated but unsealed) basement band joists etc. A blower test done before any work was done yielded .9ACH. I'm hoping we've knocked it down to .5 or so. Will test again after all the work is done.
    The plan is to put in polycinine foam under roof eaves and inside gable walls to make a non-vented attic. We have a 10ft peak in attic so it's useful as some kind of space, so we'd rather not dump cellulose on attic floor. Even with the foam I know we should seal some of the attic penetrations. I realize that the best heating efficiency might come from insulating the attic floor rather than the roof eaves etc. but we need to lower summer temps for AC handler and the 8" supply ducts that litter the floor.
    I think renting a thermal camera --rather than hiring someone--would be best. Could also locate heat piping route in basement ceiling etc.
    Thanks,
    David
  • jp_2
    jp_2 Posts: 1,935
    error in heating days
    also, a good size error can come in the spring, sunny cold days can have the same heating degree days as cloudy cold days but you can get fair amount of solar gain. same goes in the fall, we see it more in the spring though, we tend to have cloudy falls.
    this can shift real usage for a month but will become 'cloudy' when you look at the whole heating season.
  • You know, JP,
    those are excellent points that many, including myself overlook. It is easy to forget that November has more intense sun on vertical glass than in September and especially June/July, because it approaches at a low angle, more perpendicular to the glass.
    November is "I told you so" month when owners who "value-engineered" a 4-pipe system to a 2-pipe system cry for cooling when they have been heating for a month.
    Who said "November is the Cruelest Month"? Either an HVAC engineer or an owner with buyers remorse...
  • jp_2
    jp_2 Posts: 1,935
    variables
    thats what makes this stuff interesting. all those variables and you can't count on a single one!
  • D107
    D107 Posts: 1,950
    Based on degree days looks like 26% savings
    If I'm correctly reading info at wunderground.com figures for same period are:
    2005 = 437 Degree Days, 80 therms minus 14TH (nonheating) = 66Therms divide by 437DD = .151 DD per therm;
    2006 = 445 DD, 64 therms minus 14TH = 50Therms/445DD = .112DD per therm. Savings of 26%. (for cellulose, fireplace seal and lower boiler temp.)
    Now what if I varied my day or night indoor temps--I shouldn't for test's sake--but if I have to how would one calc additional usage? Based on X hours of comparative higher room temp?
    Thanks, that's really a great site.
    David
  • D107
    D107 Posts: 1,950
    I wanted to make sure I understood your point on windows...
    As far as I understand, insulating the sash pockets --where the weights/pulleys of the old wood windows are--is done by removing left and right window trim from the INSIDE. The upper and lower parts of these pockets can be sprayed with a little slow expanding foam, and then rigid insulation can be put in the rest of the pocket, or perhaps since these are replacement windows and the weights can be removed, spray foam can be used throughout.
    You say, "then add the 3/4 foam board and foam the gap between window and 3/4 foam board." The 3/4 foam board is going outside, over the existing clapboards; I don't know what you mean by the gap between window and foam board. And the foam board you say to add, is that the same foam board that's going over the clapboards?
    Thanks,
    David
  • jp_2
    jp_2 Posts: 1,935
    assumptions
    david, without 'seeing' your house, I made some assumption:
    1.) the original windows have no insulation between the window frame and the framing opening of the house.
    you can insulate this perimeter by remove all sides of inside window trim, or depending on the orignal outside trim, take the outside trim off around the windows and insulate from there. since you are moving the windows outward, i'd guess you will redo outside window trim.
    i use slow expanding foam, 3/4 of pocket. biggest point is to do reduce any air leaks with the expanding foam.
    but i agree, doing this from inside is better, but if the inside trim was in great shape, then you do not want to mess with it.
    I'm suggesting, when the foamboard is installed on old siding, leave a nice gap around the windows 3/4", then go back and 'foam-in' this gap for a better seal.
    sometimes 'ventless' attics will greatly reduce roof life do to roofs inability to cool down. seems thats what curls shingles on southern exposures. also can lead to ice dams
  • D107
    D107 Posts: 1,950
    Got it, thanks
    yeah I thought you meant foam the perimeter. I'm sure the sash pockets weren't insulated when they replaced the windows--too bad; some of the infra red photos I posted do show infiltration from header and side pockets. I'll be ready with foam during the vinyl install in case pockets are reachable from outside. Everyone tells me removing inside trim is easy--looks fine now--but it might never look as good after the crow bar.
    Thanks,
    David