zone valve water hammer
I know this has been on the wall before, please one more time.
contractor/customer called has 3 honeywell zone valves
causing water hammer when they close. boiler change out to wm ultra, primary/secondary install.
thank you in advance0 -
Bob
pull one of the retuern springs on the valve0 -
Install a pressure differential Bypass Valve
http://www.taco-hvac.com/products.html?current_category=204
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Make sure the valves aren't installed backwards. Then look here: http://www.heatinghelp.com/newsletter.cfm?Id=1370 -
Is the location...
of the ZV's on the return, or the supply - immediately in front of the circulator?
If so, you may have to change them.
The probable cause is an unmatched circ. head dynamic. We tend to use wet-rotor circs. The high heads afforded when just one ZV calling can be pretty violent on closure. By choking off the circulator output via some form of throttling device, you may be able to maintain a 20 dT accross any combination of ZV "calls" - and reduce "dynamic head pressures" to a gentler factor, quieting down ZV slam and still staying around a dT of 20F.
Got isolation valves on the supply side of the circ.? (never close the suction side isolation valve (if so equipped)) - close it until you see a dT of 20 degrees on the highest head zone. You'll be amazed at how nicely things will quiet down.0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements