Options
Christian Egli_2
Member Posts: 812
The capacity inside the boiler is not related to the steam content of the system, as you've discovered it only takes a thimble worth of water turned into steam to fill all your pipes.
What causes low content boilers to go on low water level is the slowness of the return pipes. In some systems (like large horizontal homes with low sloped returns) there can be lots of condensate just loitering around in the returns just idling back to the boiler. On shut off it eventually all returns, but with an operating volume delay - thus the need for water capacity at the boiler.
You can get a feel for that situation by observing your operating boiler and taking note of how much the level falls on start up until it reaches steady state. In the summer, you can also test all this by pouring simulated condensate at the headwaters of the returns then watch the exit hole at the boiler. You'll get a very rough idea of your return operation.
As far as your boiler selection, ask the supplier what the differential capacity is between normal operating level, low level and high level. That number may be more useful.
I would tend to prefer the higher capacity, it is less problematic without a feed tank (which is overkill in a home set up) and it is less problematic for dissolved solids concentration and blow down needs.
Happy to see you steaming.
Don't forget, all new traps are always a good idea. Have them changed / replaced along with the boiler. Choose those with the best venting stats as per the venting chart by Gerry Gill and Steve Pajek, available here online, don't just choose the most easily available locally.
Are you located in a major steam country?
What causes low content boilers to go on low water level is the slowness of the return pipes. In some systems (like large horizontal homes with low sloped returns) there can be lots of condensate just loitering around in the returns just idling back to the boiler. On shut off it eventually all returns, but with an operating volume delay - thus the need for water capacity at the boiler.
You can get a feel for that situation by observing your operating boiler and taking note of how much the level falls on start up until it reaches steady state. In the summer, you can also test all this by pouring simulated condensate at the headwaters of the returns then watch the exit hole at the boiler. You'll get a very rough idea of your return operation.
As far as your boiler selection, ask the supplier what the differential capacity is between normal operating level, low level and high level. That number may be more useful.
I would tend to prefer the higher capacity, it is less problematic without a feed tank (which is overkill in a home set up) and it is less problematic for dissolved solids concentration and blow down needs.
Happy to see you steaming.
Don't forget, all new traps are always a good idea. Have them changed / replaced along with the boiler. Choose those with the best venting stats as per the venting chart by Gerry Gill and Steve Pajek, available here online, don't just choose the most easily available locally.
Are you located in a major steam country?
0
Comments
-
Operating volume for replacement steam boiler
I have been checking operating volumes for Peerless and Dunkirk steam boilers (150 mbh input). That is the volume of water between the operating level and the low water cutoff. Called the factories and found that the Peerless claims about 4 gallons and the Dunkirk claims only 1.5 gallons. Seems that is quite a difference and that the Peerless will be a better bet to replace a large old boiler. I calculate that the volume of water needed to fill the mains with steam is only about 1/5 gallon, but that extra water in the Peerless will give a better margin of safety if the condensate is slow to return.
I am surprised at the big difference. Can anyone confirm that this is correct. Is the design of the Peerless that much different? Bigger steam chamber? I have never seen the insides of the two.
The Peerless is a few more bucks but it would seem worth it.
MarkB
Has anyone looked at this and found this0 -
Mark,
Seems like a helluva discrepency to me too. Although I am not terribly familiar with either unit's waterway configuration, I would be inclined to believe one of the two responders did not understand your question, and answered correctly - to something you never asked (:-o)0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements