Calculating efficiency of older boilers
Jesse_3
Jesse_3 Member Posts: 3
I am trying to find some information on calculating the efficiency of older style gas hot water boilers. I was wondering if there are a set of equations or some software that would be helpful. Thanks.
  • jp_2
    jp_2 Member Posts: 1,935
    easy on paper
    clock the gas meter.
    measure delta T water temp. in/out of boiler
    measure flow rate of water.in/out of boiler
    delt T x 8.33 x gallons flow = btu's boiler output
    meter clocking will give you btu's into the boiler
  • Jim Davis_7
    Jim Davis_7 Member Posts: 67
    don't forget you have to multiply gpm times 60 minutes for the BTUH.
  • johnny4
    johnny4 Member Posts: 12
    estimating efficiency
    If you don't have access to temp in and temp out, or flow rate in & flow rate out, one way to *estimate* efficiency of an old boiler is to take a combustion efficiency test result and multiply by 0.85. So if a technician performs a combustion efficiency test and says the boiler has a combustion efficiency of 84%, then the overall efficiency (similar to AFUE) is about 71% (85% x 0.85). This would account for off-cycle losses, and so forth. Of course, this requires a combustion efficiency test to begin with.
  • Okay.....
    How do you factor in whether it has a vent damper; or electronic ignition?
    How do you account for a boiler with a circulator post purge cycle? With 3" of insulation vs. 1" of insulation?
    Where did this formula come from?
    Noel