Tekmar 260 install problems
Options
Tom_81
Member Posts: 6
I'm installing a tekmar 260 on my 5 zone fin tube baseboard system with a zone valve operated indirect DHW. I'm encountering two problems:
1) I just burned up a zone valve power head while testing the system. They are Taco 570 series valves and I have 6 (5 zones plus DHW) on two 40va transformers wired in parallel. This is the second head that has failed. The first failed prior to installing the 260. Could I have two much load for the two transformers? Could it be a wiring problem? I took the inputs that were running to the Honeywell 8148 and placed them on the 260 boiler demand input with the boiler ouput from the 260 running back to the TT terminals on the 8148.
2) I'm having a tough time figuring the proper wiring for the DHW demand and DHW valve output. I know I need to run the DHW aquastat to the demand input on the 260, but it has to be powered. Where in the loop between the aquastat, DHW zone valve (again, a Taco 570 series) and transformer does the 260 sit?
Thanks, I appreciate the help. My wife isn't liking the cool showers and burning up power heads is kind of defeating the whole efficiency, cost savings thing!
1) I just burned up a zone valve power head while testing the system. They are Taco 570 series valves and I have 6 (5 zones plus DHW) on two 40va transformers wired in parallel. This is the second head that has failed. The first failed prior to installing the 260. Could I have two much load for the two transformers? Could it be a wiring problem? I took the inputs that were running to the Honeywell 8148 and placed them on the 260 boiler demand input with the boiler ouput from the 260 running back to the TT terminals on the 8148.
2) I'm having a tough time figuring the proper wiring for the DHW demand and DHW valve output. I know I need to run the DHW aquastat to the demand input on the 260, but it has to be powered. Where in the loop between the aquastat, DHW zone valve (again, a Taco 570 series) and transformer does the 260 sit?
Thanks, I appreciate the help. My wife isn't liking the cool showers and burning up power heads is kind of defeating the whole efficiency, cost savings thing!
0
Comments
-
Break down,
bite the bullet.
Power the 5 Taco's with an 80 VA transformer.
Part 2? You may simply want to get a 5 zone TACO relay.
The 260 requires an isolation relay for the circ. If I recall correctly. Remember, in most instances, the stat does not turn on the control, it merely "makes" the device circuit.
THEN, the device has an end-switch which makes the burner or control circuit - after it has been activated from the primary circuit...
Again, it's been a while, but I recall the 260 having a d/h/w priority dip switch. Make sure that's "on."0 -
I'll second the motion for replacing the two transformers in parallel with a single transformer of sufficient capacity. Have dealt with parallel transformers before and they seem to have problems. Like water heaters in parallel they don't seem to share the load equally...0 -
Thanks guys.
So, running two underpowered transformers in parrallel - not so good, huh? I'll price an 80va transformer.
I solved my wiring issues thanks to the good help of Mike at tekmar. Something about wiring a red lead into a bunch of white wires that I just couldn't do without a little technical support. I know the color of the jacket doesn't really matter, but....
Thanks again.0 -
Tom....
....you're most welcome.
Just call, should you have further questions and comments. And thank you for calling back to let me know all went well.
Regards,
MikeThere was an error rendering this rich post.
0 -
Do yourself a favor
In my opinion, do yourself a favor and get the Taco 406 control. You will thank yourself down the road...0 -
Tekmar
Wiring two 40va transformers in Parallel should NOT burn out a power head, unless your accidently wiring the secondaries in series instead of parallel--effectively doubling the voltage instead of the current capability!
Pete0
This discussion has been closed.
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 120 Geothermal
- 169 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements