how to get air out of my closed loop boiler system
in addition to what Tim said, make sure that the expansion tank is connected as closely upstream of the circulator as possible.
Then, once the bulk of the air is vented, heat the water to at least 150 degrees if not to limit (180 or 200 F.). This will drive most air out of solution.
As a finishing touch, an ounce of Dawn dishwashing detergent (thanks, ME), will break down any remaining air into very tiny bubbles and leave your dishes sparkling clean! (tm).
  • mike d chicago
    mike d chicago Member Posts: 1
    removing air out of my closed loop boiler system
    I,m getting alot of water flowing noise from my closed loop bryant hot water boiler. This noise is comming from the upstairs living area and not the boiler itself. I feel as though it is air trapped in the hot water pipping and the things?? that remove the air are not working. How do I drain or bleed the air out and locate the parts that normally do this???
  • Timco
    Timco Member Posts: 3,040
    what pressure are you running at? 15psi is normal for 2-story. If CI rads, bleed air from the rads. If BB, purge the zones.
    Tim
    Just a guy running some pipes.
