Ergomax, boiler reset and mixing valves:
                
                    Chris_80                
                
                    Member Posts: 1                
            
                        
            
                    We are considering replacing our Amtrol WH-7 Boilermate with the Ergomax E23 with our Slant / Fin Victory VSPH 120.  The Ergomax will obviously supply DHW, but it will also serve as a buffer tank to help prevent boiler short-cycling.
My questions are as follows:
1) Our boiler has an outdoor temperature reset control which maintains 150  180 depending on the outside temp. The control does have DHW priority which overrides the reset temp when there's a DHW demand. If the boiler loop is at the low end of the reset curve (150*) and we have 2 showers running, is our boiler large enough to supply the 2 showers and at the same time satisfy the 170* water temp in the Ergomax?
2) I have several choices for an ASSE 1017 rated Mixing valve- do you have a recommendation for any of the following manufacturers: Danfoss, Taco, or any others?
3) Is it bad practice to reset the boiler temp when used with a reverse indirect tank like the Ergomax?
4) How does the Boilermate Wh-7 compare to the E23? From a DHW perspective, the boilermate has been able to meet our DHW demands even with the reset temps. If the E23 and the WH-7 are similar in performance, we shouldn't have a problem.
Hope these questions make sense -
                My questions are as follows:
1) Our boiler has an outdoor temperature reset control which maintains 150  180 depending on the outside temp. The control does have DHW priority which overrides the reset temp when there's a DHW demand. If the boiler loop is at the low end of the reset curve (150*) and we have 2 showers running, is our boiler large enough to supply the 2 showers and at the same time satisfy the 170* water temp in the Ergomax?
2) I have several choices for an ASSE 1017 rated Mixing valve- do you have a recommendation for any of the following manufacturers: Danfoss, Taco, or any others?
3) Is it bad practice to reset the boiler temp when used with a reverse indirect tank like the Ergomax?
4) How does the Boilermate Wh-7 compare to the E23? From a DHW perspective, the boilermate has been able to meet our DHW demands even with the reset temps. If the E23 and the WH-7 are similar in performance, we shouldn't have a problem.
Hope these questions make sense -
0                
            Comments
- 
            Ergomax
has some pretty good output tables at various temperatures and flow rates.
2 showers at the same time?... doubtful unless you have very low flow (gpm) shower heads.
A dealer or repshould have the data to help you decide. They need a bit of horsepower and tempersture to perform at peak.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 
This discussion has been closed.
            Categories
- All Categories
 - 87.2K THE MAIN WALL
 - 3.2K A-C, Heat Pumps & Refrigeration
 - 59 Biomass
 - 427 Carbon Monoxide Awareness
 - 118 Chimneys & Flues
 - 2.1K Domestic Hot Water
 - 5.7K Gas Heating
 - 113 Geothermal
 - 164 Indoor-Air Quality
 - 3.7K Oil Heating
 - 73 Pipe Deterioration
 - 1K Plumbing
 - 6.4K Radiant Heating
 - 393 Solar
 - 15.5K Strictly Steam
 - 3.4K Thermostats and Controls
 - 56 Water Quality
 - 51 Industry Classes
 - 49 Job Opportunities
 - 18 Recall Announcements