staged setback for AC

Options
archibald tuttle
archibald tuttle Member Posts: 1,163
I have a 15 ton chiller with two compressors that provides water to fan coil room units in an 8 apartment facility. I have been idly (less idly as the price of energy rises, funny how the market works) seeking a setback (or set forward if speaking metaphorically) controller to moderate water temperature as outdoor temperaturs cool, provide cool weather shutdown when a comfort threshold is reached, and stage and swap lead between the compressors. In other words do everything for a cooling system that a TACO PC-702 does for a heating system.

My early inqueries have not produced any control manufacturers who were making controls of this sort, although perhaps I overlooked AC control specialties as the vast majority of my HVAC work is on the heating side. While the range of adjustment of temperature call would be much more modest than in the heating circumstance, I imagine it would still lead to some efficiencies and most of the internal zone valves on this system are locked open as they rust up and Trane made them virtually impossible to replace at a labor cost and approach that is much less than buying an entire new fan coil every time the freaking zone valve drops out. Anyway, moderating water delivery temperature in line with outdoor temperature would allow consistent fan speeds and less oscillating for tenants. It works great in the winter and the loss of room by room themostatic control has gone virtually unnoticed.

For the few rooms that are outliers to this trend because they have signficantly different losses and units weren't sized quite so well, we use aftermarket thermostats to turn fans on and off instead of zone valves. Way easier than messing with the zone valves. Don't know if Trane has improved their designs since these were installed (maybe 35 years ago) but I couldn't ever recommend buying one of their units based on these that I have to service.

Brian

Comments

  • Empire_2
    Empire_2 Member Posts: 2,340
    Techmarcontrols.com

    Try this sight. I am sure they will have what you are looking for. Your compressor swap is called "Lead Lag" control.. Sounds like the trane unit has no temp control on the inlet and outlet to the barrel. Is this the case? That would mean the thing runs wide open until Something shuts it down...

    Mike T.
  • archibald tuttle
    archibald tuttle Member Posts: 1,163
    tekmar

    Thanks for the thought. I am pretty sure I asked a Tekmar rep who was doing a powerpoint demonstration on their new multithermostat multi output control systems this past fall if they had an AC solution and he said no, but it never hurts to try, given that I can't remember some stuff I did yesterday, I may be misremembering my discussion with him.

    As to the Trane unit running wide open, there are actually two 'trane units' involved. The chiller is a trane unit. Don't know much about its relative efficiency. It is about 15 to 18 years old. It currently runs with a very simple analog lead/lag control that kicks in the second compressor if the difference between the inlet water temp and the setpoint is 5 degrees. I put in a 3 way swith that I switch every season to alternate which is lead and which is lag.
    the setpoint itself has no adjustment mechanism other than physical changing. In that sense we leave the setpoint at around 38 degrees and it runs 'wide open' to make this setpoint throughout air conditioning season. There is no compensation for outdoor temperature (although obviously it will run less to make the setpoint when outdoor temperatures are cooler).

    The fan coil units inside are also Trane units and they are designed (typically, I can't blame Trane for the basic idea) so that the fan runs all the time and there is a zone valve that admits the conditioned water when the room air temp calls the valve through a thermostat integrated in the unit. The thermostat is a volatile fluid probe placed in the path of room air returning to the unit along the floor just inside the air filter. There is an electrical comparator that senses the water temperature offered by the circulating water, presumably for shoulder seasons when one room might want cooling but the heat is actually on so opening the zone valve would be counterproductive.

    These fan coil units are older than the AC chiller (which has been replaced once during the life of this system - maybe it is due for replacement again if efficiencies have been markedly improved maybe by two smaller units more like stage boilers.) Anyway,the fan coils are about 35 years old and there is not one that has a working zone valve on it anymore. There were no unions or replacability built into the design of the unit and there is very little spare pipe providing for installing any kind of update. It is remotely conceivable that you could remove the zone valve workings from the valve body and retrofit some carefully organized replacement but service access is miserable and the wiring is substandard (old mtw, not thhn, I consistently get units where the wire coatings give inside flexible metal conduits and short out.) The addition of operational voltage (all 120 AC, including fan motor and zone valve) water temperature sensors and wiring to the zone valve is just another nightmare. Generally, once a unit melts down I just cut the zone valve out, eliminate the wiring harnes and pipe straight over (not easy to do either because the piping employed on the unit side of the zone valve is like copper foil. Far thinner than even 'm' tubing and subject to damage from cutting and attempts to swage or otherwise make it possible to attach regular copper fittings)

    These have to be some of the worst designed things I've ever dealt with, but I know it was pretty much par for the course in those days and Trane was the 'cutting edge'so I'm not out to suggest that any other company would have been better since I do not know.

    Brian
  • Empire_2
    Empire_2 Member Posts: 2,340
    Brian

    Sounds interesting. I think I have worked on this Trane unit before, (not Yours) but only larger...40 ton. If you want, You can call me at the office, leave a message and # if I am not in. I would love to get to the bottom of this thing. If you can, raise your set point to 41/43* and diff to about 6 to 9*. with a wider diff the building load on a cooler day should not kick in the 2nd compressor. You almost have to play with the settings to find a happy medium..

    Mike T. Empire Mechanical 716-648-1763
  • John Mills_5
    John Mills_5 Member Posts: 952
    Cycle the fans?

    Since there is no temp control of the units anymore, can a thermostat be used to cycle the fan off when stat is satisfied?