47-2 lwco with autofill hammering at end of feed
rick_29
Member Posts: 5
I had a similiar problem .Iinstalled a tee with a arrestor and it worked But also see if you have a pressure reducing valve, it may be bad, I had city water pressure at 150 and the reducing valve failed .something to look at
0
Comments
-
47-2 lwco with autofill hammering at end of feed
Hi, I have a customer with a 47-2 lwco and autofill (both brand new) that, at the end of a feed, begins to flutter or hammer the inlet water line loudly. My guess is that because of the mechanical design of the fill, it does not shut off immediately like a solenoid type. Will a water hammer arrestor solve this? It flutters for a good 20 seconds. thanks, scott0 -
47-2
Try disconnecting the piping on the boiler side of the LWCO and check for restrictions. You'll probably find a scale build-up right at the nipple that enters the bottom of the boiler. Clean and flush this conection. Usually this causes the boiler to overfill. You could also do a broken union test on the LWCO. If he valve closes with out hammerring during the test, the feeder is OK and start looking for the restriction.0 -
incomming water pressure
Try throttling the incomming water valve down. Too much pressure will cause this.0 -
I agree throttle it down
and also make sure all the piping is secure. Some good pipe insulaTION and strapping will quiet things down too./ M ad Dog
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
#47-2
Make sure that your piped in properly. If you pipe it in backwards you'll get the same flutter while it's trying to close.
Anthony0
This discussion has been closed.
Categories
- All Categories
- 85.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 424 Carbon Monoxide Awareness
- 72 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 129 Geothermal
- 160 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 878 Plumbing
- 5.9K Radiant Heating
- 375 Solar
- 14.6K Strictly Steam
- 3.2K Thermostats and Controls
- 58 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements