Gravity RE-Conversion---Any advice appreciated
gasfolk
Just saw your post (I have to learn to type faster, perhaps with two fingers). You may be right, and we don't disagree with you.
Just wondering whether a "front-end" boiler to cover a reduced heat loss could be efficient even with our gravity flow, which recently worked well. We only gave up gravity flow because the installer said it would be more efficient, but we didn't see that.
With the older boiler as a tank (as described below), it could also provide heat in a power failure.
Thanks,
gf
Thanks,
gf
Looking for experience with gravity systems...
We may restore a "whole-house," gravity-flow zone, using ODR, on-off injection from a buffer tank, and a manifold off the injection pipes for two small RFH zones.
Our thinking: gravity flow could provide constant circulation and eliminate check valves, a circulator, and electricity. Our heat loss is small compared to the capacity of the pipes and radiation, and the house is massive--a pretty big thermal flywheel.
Could we simply pipe the gravity supplies and returns together and eliminate the over-sized, 25-gallon, CI boiler, or do we need a tank (size?) to receive the buffer injection and establish/maintain gravity flow??
Is Gravity "Self-Balancing"?? Compared to a (south-facing) room with low heat loss, will a high-heat-loss (north-facing) room draw more Btus from radiators, cool the water more, and increase gravity flow (and Btus) to that room? If so, could we skip the TRVs (and is this why the Dead Men could design balanced gravity systems without computers)?
Thanks,
gf
Anyone experienced with gravity systems...
Thanks,
gf
Anyone experienced with gravity systems?
Thanks,
gf
Spoke with a designer...
but gravity systems are rare in his area. If no one has experience UN-doing a gravity conversion, may have to just wing it.
Thanks,
gf0 -
Gravity
Gravity systems should be converted to forced circulation when changing out the boiler. A mixing device needs to protect the new boiler from thermal shock. I always use a 4 way mixing valve and a system bypass. Each boiler manufacturer has their own schematics for their preferred method. You should always consider changing the radiator valves to TRV's for precise balancing. We also put an outdoor reset control on all boiler systems. Gravity systems have their nuances. Dan H. has written extensively on gravity conversion, and John Siegenthaler has also discussed correct piping and control methods.
Check out the Heating Help Hot Tech Topics.
Hi Paul,
Thanks for responding. We are adding a reverse-indirect DHW. The indirect/buffer will isolate the boiler loop from the sytem loop. An on/off injection pump will supply the system loop from the buffer.
A number of Dan's papers suggest that gravity flow can be substantial and that the large pipes on gravity systems may need lower flow rates. Is there a way to calculate or guesstimate whether gravity flow in an isolated system loop would be adequate and whether it would satisfy the goal of continuous flow? Would a tank increase the driving force?
Good advice, we will re-read Dan's gravity-related papers in Heating Help Hot Tech Topics (easier to find with the new search feature).
Thanks again,
gf0 -
Really don't believe that it's practical to retain the gravity flow with a modern boiler. Yes, you'd need a decent sized tank of water with HUGE tappings. Beyond that if you force-circulate water into the tank, you'd most likely upset the forces that create gravity circulation through the system.
Solve those problems, and there's still another highly possible problem. The piping is certainly rougher than when it was installed. Rougher piping means more resistance to flow. More resistance to flow means you have to increase the motive force. The ONLY way to increase that force via gravity is to use hotter supply water.
In theory at least, gravity systems could perhaps have a limited self-balancing in the way you suggest but such is NOT mentioned in any of my old texts. The dead men weren't dumb. In rooms identical other than orientation they'd put in a bit more EDR in a north-facing vs. south-facing room.
The goal of gravity sizing was constant velocity in the mains and branches regardless of their length or altitude above the boiler. Combine constant velocity with radiators well sized to their portion of heat loss and you have a very balanced system.0 -
Hi Mike,
> Solve those
> water.
> south-facing room.
> was _I_constant velocity_/I_ in the mains and
I agree
I'd also trust modern boiler design without having to add a buffer tank. It's just too easy to install the boiler, control, indirect, 4 way, pressure bypass differential and system bypass. Or, if an integral boiler control is not available, using the Tekmar controls for injection and indirect DHW tank. Uses less pumps, less electrical energy, less maintainence costs.
Hi Mike,
Thanks for your good insights. An option we face is to leave the old boiler as a tank 1) to support gravity flow (there is also a lot of water in the supply pipes), 2) to cast off at least some heat into the basement (otherwise we'd have to install a separate heating loop to do this), and 3) to avoid the cost of removal.
If the buffer injects to the top of the old boiler (or even into the exiting supply pipe) and returns from the old boiler return piping, might that avoid undesirable effects on thermal stratification in (and gravity flow through) the old boiler?
Agreed, the Dead Men weren't dumb. That's one reason we are reconsidering gravity flow. The house heated fine before the conversion, and fuel use substantially increased after (probably from worsened short-cycling, now corrected to baseline fuel usage).
You experience with radiator output got us thinking... Standard CI radiator output equations suggest no output below about 100F supply, yet our house heats fine at those temps. Any equation estimating gravity flow would be interesting, but based on your observations, it may not exist. Any ideas where we might find one?
Hoping that an efficient, smaller boiler can coexist with gravity flow is unorthodox, but your experiences make us ask the question: why not? Why not try?0 -
Hi Mike,
Hi Mike,
Agreed, the Dead Men weren't dumb. That's one reason we are reconsidering gravity flow. The house heated fine before the conversion, and fuel use substantially increased after (probably from worsened short-cycling, now improved to baseline fuel usage by adding controls to widen the boiler differential).
Hoping that an efficient, smaller boiler can coexist with gravity flow is unorthodox, but your experiences make us ask the question: why not? Why not try? Of course, being homeowners, we'd first like to find data to support the experiment.
Thanks,
gf0 -
Hi Mike,
Thanks for your good insights. Could leave the old boiler as a tank 1) to support gravity flow (there is also a lot of water in the supply pipes), 2) to cast off at least some heat into the basement (otherwise we'd have to install a separate heating loop to do this), and 3) to avoid the cost of removal.
With buffer injecting to the old boiler's top and drawing from the bottom, might thermal stratification (and gravity flow) be sustained? The pipes are huge, we've improved the shell, heat loss appears low, might accumulating frictional losses be marginal?
Agreed, the Dead Men weren't dumb. The house heated fine before the conversion, but fuel use substantially increased after (from worsened short-cycling, now improved to baseline by controls to widen the boiler differential).
You experience with radiator output got us thinking... CI radiator equations suggest no output below about 100F, yet our house heats fine at those temps. An equation estimating gravity flow may not exist but would be interesting. Any ideas where we might find one?
Hoping that a smaller, more efficient boiler can coexist with gravity flow is unorthodox, but your posts make us ask the question: why not? Why not try? Of course, being homeowners, we'd FIRST like to find data to support the experiment.
Thanks,
gf0 -
Hi Mike,
With buffer injecting to the old boiler's top and drawing from the bottom, might thermal stratification (and gravity flow) be sustained? The pipes are huge, we've improved the shell, heat loss appears low, so might accumulating frictional losses be relatively small?
Agreed, the Dead Men weren't dumb. The house heated fine before the conversion, but fuel use substantially increased after (from worsened short-cycling, now improved to baseline by controls to widen the boiler differential). Back where we started, except gave up gravity flow.
Thanks,
gf0 -
Hi Mike,
Your experience with radiator output got us thinking... CI radiator equations suggest no output below about 100F, yet our house heats fine at those temps. An equation estimating gravity flow may not exist but would be interesting. Any ideas where we might find one?
Hoping that a smaller, more efficient boiler can coexist with gravity flow is unorthodox, but your posts make us ask the question: why not? Why not try? Of course, being homeowners, we'd first like to find data to support the experiment.
Thanks,
gf0 -
I've tried before to come up with a workable plan for such a forced/gravity hybrid. Problem is that you'd still have forced flow through the tank (or wherever you have a decent volume of water). Injecting to the top and drawing from the bottom would set up a counter-flow situation and I HIGHLY suspect that the forced injection would "win". You'd just be re-circulating the same BTUs through the injection loop with VERY few of them leaving the system via gravity flow. Injecting at the bottom and drawing from the top [might] be a better situation, but again I very much suspect that too many of the BTUs will just circulate through the injection loop. The flow will GREATLY favor the circulator path with its relatively high pressure differential! Don't forget that you'd need HUGE tappings for the gravity connections. A small bottleneck doesn't bother forced flow too much, but gravity isn't so forgiving.
Yours and MANY others. Those old tables are invalid at lower temperatures!
Such certainly exists! Write me with your fax number and I'll send that information from a relatively modern book. You'll be working in rather unusual measures including milinches (1,000ths of an inch) instead of FEET of head, and inches per second of velocity instead of FEET per second. You'll also be using pounds per hour water flow.
A typical two-floor gravity system generally operates with only about 2 INCHES of pressure differential on the TOP floor--about half that on the ground floor! This with a 30° delta-t. Lower delta-t means less differential. See why I suggest that a circulator anywhere in the system will cause problems?
Interesting....
PAUL: We read your PRO page. Very nice work, and if we didn't have issues with this structure, existing equipment, etc., that would be a great way to go. For a new house, we KNOW you are right. Still, since we've inherited a gift from the Dead Men--a functioning gravity system--and since they don't make them anymore, we're wondering whether modern boiler can marry beautiful (but elderly) gravity heat distribution?
MIKE: Old boiler is EGH-85: two 2 1/2" supplies, two 2 1/2" returns--minimal flow restriction? It holds 25 gallons, but even if circulator flow initially overcomes gravity flow, then boiler water temp will rise, and at some point won't gravity flow up the supply pipes carry heat into the system? Used to work as efficiently as current piping (not saying much).
With the frequency that check valves are recommended to stop gravity flow, we're (ok, I am) tempted to see if our old beast could work with the new smaller boiler. Too bad there is no observational data on whether a big tank can decouple circulator and gravity flow?? Very interested in your equation (will send fax # offline).
Thanks guys.
gf0 -
4 x 2½" connections doesn't sound like much flow restriction to me... The boiler tappings may well be bushed down from 3" as well. Those are larger and more taps than available in any modern boiler of proper size. I seriously doubt any reasonably sized buffer tanks have such tappings either.
Hate to bring this up, but isn't your real problem an extremely oversized boiler? 2½ - 3x oversized comes to mind. Know you now have a buffer tank to try to address the problem. If anything gravity flow would probably make the oversizing worse because forced flow will move heat MUCH faster. Don't forget that your converted gravity system can likely still immediately absorb the energy of even a greatly oversized boiler and liberate it nearly as fast. Transmission and liberation of heat aren't your problem--you simply have WAY too much energy available even the the coldest weather and since the boiler can only fire or not fire, it would take an ENORMOUS buffer to effectively dampen that roaring beast.
Gravity mains [can] act as a sort of buffer, but the conditions are strict:
1) There must be continuous circulation.
2) That continuous circulation MUST BE SLOW--either via gravity or controlled via TRVs. A "wide open" gravity system with the typical B&G 100 moving 25 gpm or so has a dampening as opposed to buffering effect.
3) Even though the pipes are huge and hold quite a bit of water, the "buffer" does not have the buffering ability of a tank of the same size. The "buffer" will be fully charged VERY RAPIDLY with a non-modulating boiler.
In my system (with a Vitodens) the buffer only works within a limited range of system load. As far as I can tell, I get about 7,000 BTUs of "buffer" capacity with the "buffer effect" working in a 14,000 btu range. It ONLY works when system load (heat loss) is in the approximate range of 11,000 - 25,000. Above 25,000 the boiler modulates and the mains act as a damper instead of a buffer.
When heat loss drops minimum modulation, the mains begin to act as a buffer. The excess energy accumulates in the mains while the burner fires and is liberated after it stops firing. This is an inverse relationship--the more slowly it accumulates the more rapidly it is consumed.
Once heat loss drops below minimum modulation minus "buffer capacity" (25 - 7 = 18 mbh) the "buffer" begins to charge faster than the remaining output is being liberated by the radiators. Firing times become shorter and shorter. Once loss drops to minimum modulation - "buffer effect" (25 - 14 = 11 mbh), it seems to loose all effectiveness and the boiler operates in continual "pulse" mode delivering very short bursts of full output with the mains again acting as a damper.
Offered for your approval ...
You are correct, the old boiler is about 7 times design load. The idea is never to fire (we hope) the old boiler, only to take advantage of it.
To try to restore gravity flow... Rather than spend to remove the old boiler, and then spend on a Bock (or other) storage tank, and then spend some more on a heating loop for the basement, perhaps the old boiler can be both gravity tank and backup boiler (in case all our sizing calculations prove wrong--not likely).
In sizing for DHW, the new, much smaller boiler will still have a minimum output at least 60% of our design heat loss, and will be oversized most of the heating season. Buffering through the reverse-indirect should limit short-cycling, with heat injected from the indirect to the "gravity tank" (i.e. old boiler).
An idea perhaps only risk takers would embrace?? Can always repipe if it fails miserably??
Thanks for the thoughtful criticism and suggestions,
gf0 -
things i have seen...
some poor people just lash things up and they work and have no clue whats what or the math or science behind any of it they just figure 'well, we need heat!'
hey and it works:) been working 30 years
lashed into old gravity systems printed beacoup d years ago.
too lazy or not enough time to remove the old boiler they just tied right into it ...of course laying in all kinds of 1/2" pex was not on the agenda:) just something to think about...0 -
\"Wake UP! Meditations OVER! Kebadachi!\"
Thanks Mike, Paul, and Weezbo (really enjoyed your "Kebadachi" comments) for responding.
Although our current boiler is technically "the old boiler," Weil Mclain "commercial" EGH-85's are still installed today. Sure, ours is over-sized, but we've had such trouble convincing contractors that our heat loss is below Manual-J estimates, keeping it seems easy insurance.
We hate to see old systems (steam, gravity, whatever) destroyed before understanding their design and function and whether modern equipment can keep them working efficiently. Just asking a lot of questions. Sorry if our posts suggest haste, laziness, poverty, or lack of clue.
Our copy of "Heating design and practice," (by Robert Henderson Emerick, McGraw Hill, 1951) should arrive early next week. Currently reading Siegenthaler's "Modern Hydronic Heating".
Thanks again for raising issues to consider.
Best regards,
gf0 -
Thanks Mike, Paul, and Weezbo for responding. (Weezbo, we really enjoyed your "Kebadachi" comments, among many others.)
Although our current boiler is technically "the old boiler," Weil Mclain "commercial" EGH-85's are still installed today. Sure, ours is over-sized, but we've had such trouble convincing contractors that our heat loss is below Manual-J estimates, keeping it seems easy insurance. [Hey, maybe they're right--we're just homeowners.]
Best regards,
gf0 -
Reading list?
Weezbo, too bad those folks didn't keep track of how well or poorly their lashed up system worked. Their experience could have been interesting.
We're open to suggestions for readings about gravity system design (probably only in old texts, like the Dead Heat Scrolls?).
Thanks,
gf0 -
Have still been pondering...
One SERIOUS concern with using the old boiler that way is that it will turn into the most efficient radiator in the house with the heat going right up the flue... I suppose you could disconnect and plug the boiler flue--then at least it will just be a radiator heating the basement...
While I could very well be wrong, I still suspect that the gravity flow will be disrupted when you move forced flow through the boiler. It might work and I guess you've lost little by trying.
You seem to be willing to try anything to avoid using TRVs. Their cost really isn't that high. Believe you have one or perhaps two 1 1/2" valves to contend with, but such really isn't that serious of a problem. I've yet to meet a gravity pipe that I cannot remove and I've honestly only crushed one pipe--that a 1" pipe with a 36" wrench and 48" cheater bar. That was a system with some sort of hardening, almost cement-like dope. Found a solution--repeated dousing with cheap (mainly petroleum distillate) silicon spray. You may even be able to avoid "shifting" the location of the radiator by using two reducing bushings at the radiator taps. (That presuming the rads have 2" taps--if they're 1 1/2" you need a bushing anyway.)
Hi Mike,
Great points. We're still open to TRVs, and rather than every radiator, perhaps on a selective basis if we find imbalance (overheating?) with the new boiler installed?
Weezbo's right. We're going to just try it, and will post the results next heating season. We predict it won't work because of the concerns you raise, but the opportunity to experiment is just too tempting (don't tell the wife).
Still working out small details before repiping in June. Thanks for your good ideas. Makes us want to choose the injection ports carefully.
gf0 -
Please don't even think that you could use TRVs to eliminate overheating on selected rads using gravity flow.
Check the cv ratings of even the least restrictive TRVs against that chapter I faxed you and you'll see that they'll halt flow through the associated branches. The piping itself consumes most of the available force leaving almost nothing for restriction in the valve or the radiator.0 -
Gravity system balancing...
Hi Mike,
So, to leave open options for balancing (if necessary), we will plan piping for forced circulation before considering TRVs.
Did the Dead Men have a way to balance a gravity system after installation? That they adjusted radiator size to some extent for room heat loss is visually apparent. Is there a way to find evidence for a balancing effect of gravity flow? Would it be convincing to compare room-to-room EDR and room-to-room heat loss, the latter estimated by the best current software and climate estimates, but using historical building details? What discrepancy would convince that gravity flow balancing was present?
Thanks,
gf0 -
bump0 -
After installation? Perhaps those restrictor plates in upper floor radiators?
Other balancing tricks I've read of and/or observed include:
1) Compensation for the construction of the radiator. Two-column and low "window" rads were known for relatively high output compared to rads of other types. 4-column was the relative worst. Two old books tell me that many of the column-type rads were rated based on actual surface area--as testing improved surface area became arbitrary to rating. All tube-type rads were rated this way.
2) Compensation for the placement of the radiator. If placed on interior walls, they often added 15-20%.
3) Compensation for any planned covers. Depending on the design of the cover, the rad size could change considerably--usually significantly larger.
4) Compensation for other heat sources. Kitchen rads were frequently omitted or greatly undersized to compensate for the big iron cookstove.
5) Compensation for comfort/lifestyle. Bathroom rads were frequently oversized. Bedroom rads were sometimes oversized--I suspect to facilitate recovery after the daily "airing" and/or sleeping with an open window--both fairly common practices.
6) Compensation for fresh air intake. Many rads were available with a "direct-indirect" option. The rad sat on top of a "box" with dampers to both the indoors and the outdoors. The dampers operated in unison to allow indoor air, outdoor air or a mix. Obviously these rads were increased in size to compensate for the cold, outdoor air.
7) Compensation for ceiling height. With ceiling above 10' or so, progressively more EDR was added above the increase in volume/exposure. Evidence of this is VERY common in open stairhalls--especially pronounced when any portion of the staircase was on an outside wall.0 -
Agree with the following quotation?
Hi Mike,
Very interesting list. Does the lack of a post-installation compensations explain the Dead Men's detailed calculations or might it support an element of self-balancing?
The delta T from radiator to room will be higher in a shaded, northern room than in a sunny, southern room; more Btus will hop off into the northern room, cooling the water more, and increasing gravity flow; fewer Btus will escape into the sunny room, maintaining radiator water temp, and reducing gravity flow?? Flows too low to measure, but perhaps enough to fine-tune a well planned system?
We're impressed that Wallies with special skills can preserve functioning steam systems. If the Dead Men designed well, could special skills save gravity circ (i.e. free, constant circulation) on boiler retrofits? Could gravity circ (and the expense of larger pipes and planning) be touted as the true high-end system? Or does everyone generally agree with this opinion...
"Gravity systems...tend to heat unevenly, are slow to respond,...are considered inefficient and normally should be replaced during the rehabilitation process."
(Source: http://www.oldhouseweb.com/stories/Detailed/10463.shtml)
Thanks,
gf0 -
Hi Mike,
Very interesting list. Does the lack of a post-installation compensation explain the Dead Men's detailed calculations or might it support an element of self-balancing?
Thanks,
gf0 -
Hi Mike,
We're impressed that Wallies with special skills advocate to preserve functioning steam systems. If the Dead Men designed well, could special skills save gravity circ (i.e. free, constant circulation) on boiler retrofits? Could gravity circ (and the expense of larger pipes and planning) be touted as the true high-end system? Or does everyone generally agree with this opinion...
Thanks,
gf0 -
Other questions...
1) Does data support the claim that converting a gravity system to forced circulation will save a significant amount of fuel?
2) As long as the boiler loop is pumped for maximum boiler efficiency, how much could efficiency improve with circulator vs gravity flow in the system loop?
3) When two loops mix in an hydraulic separator (e.g. Callefi or our 25 gallon "old" boiler), why would a gravity-flow loop NOT be decoupled from a pumped loop? If disruption of flow is peculiar to gravity loops, is that because flow is too low in a gravity loop? Or does a garvity loop appear different to a hydraulic separator in some other way?
Thanks again,
gf0 -
Other questions...
1) When is it true (and is does data support the claim) that converting a gravity system to forced circulation will save a significant amount of fuel? As long as the boiler loop is pumped for maximum boiler efficiency, how much could efficiency improve with circulator vs gravity flow in the system loop?
2) When two loops mix in an hydraulic separator (e.g. Callefi or our 25 gallon "old" boiler), why would a gravity-flow loop NOT be decoupled from a pumped loop? If disruption of flow is peculiar to gravity loops, is that because flow is too low in a gravity loop? Or does a garvity loop appear different to a hydraulic separator in some other way?
Thanks again,
gf0 -
Other questions...
1) When is it true (and does data support the claim) that converting a gravity system to forced circulation will save a significant amount of fuel? As long as the boiler loop is pumped for maximum boiler efficiency, how much could efficiency improve with circulator vs gravity flow in the system loop?
Thanks again,
gf0 -
Other questions...
1) When is it true that converting a gravity system to forced circulation will save a significant amount of fuel? As long as the boiler loop is pumped for maximum boiler efficiency, how much could efficiency improve with circulator vs gravity flow in the system loop? Is there data supporting this claim?
Thanks again,
gf0 -
Other questions...
2) When two loops mix in an hydraulic separator (e.g. Caleffi or our 25 gallon "old" boiler), why would a gravity-flow loop NOT be decoupled from a pumped loop? If disruption of flow is peculiar to gravity loops, is that because flow is too low in a gravity loop? Or does a gravity loop appear different to a hydraulic separator in some other way?
Thanks again,
gf0 -
The only unconverted gravity system I've felt was slow, not particularly even and definitely inefficient (original coal boiler converted to gas). All the rest I've felt/worked on were converted to forced flow LONG ago.
"Slow response" was ALWAYS stated as a problem with gravity systems--this required that the fire be carefully tended, to include attempting to anticipate the weather. While a modern burner and thermostat helped with that problem, I really can't imagine that it does do efficiently.
That chapter I sent you regarding the mathematical design of gravity systems is relatively modern (1951). The earlier texts are different. While the more involved do touch on such design, they generally concentrate on the "valve area" design method.
"The delta T from radiator to room will be higher in a shaded, northern room than in a sunny, southern room; more Btus will hop off into the northern room, cooling the water more, and increasing gravity flow; fewer Btus will escape into the sunny room, maintaining radiator water temp, and reducing gravity flow?? Flows too low to measure, but perhaps enough to fine-tune a well planned system?"
There [seems] to be some serious problems with that theory. Yes, output will go down in a sunny room--but only after it is overheated! I cannot however imagine that those "unused" BTUs just magically hop into underheated spaces. Yes, output will go up in a cool room, but you've already assumed that its' underheated! The goal was to avoid such underheated areas to begin with!
Modern boilers simply are not designed for gravity flow so you have to go to extraordinary lengths to imitate an old boiler--effectively a big tank with HUGE openings out the top and near the bottom. Then you have to get heat into that tank in a way that won't disrupt gravity circulation. Honestly seems both impractical and inefficient to me...
I'd NEVER replace a gravity system--instead preferring to bring it into the modern age with a condensing/modulating boiler and TRVs. This produces a system that the Dead Men could only dream about. Plus, any imbalances caused by poor design, added insulation, roughened pipes, etc. will completely disappear.
I honestly can't answer those questions.0 -
Thanks Mike,
Your analysis of buffering seems to explain why our gas use increased after conversion from gravity flow to injection mixing with a 0010 circ. Is your Vitodens with small circ simply piped in series with your old gravity system, and do you believe you are getting the benefits of that buffering (reduced short-cycling) during shoulder seasons. Maybe that is the setup we should be considering.
gf0