nozzle angle when you increase pressure
burnerman_2
Member Posts: 297
well the droplets decrease in size but the angle stays the same patterern royboy
nozzle angles
what happens to the angle of a nozzle when you increase pressure at the pump?0 -
I disagree royboy.
When the pressure increases, the spray pattern will follow suit. If an 80° nozzle is speced. at 100psi, why would almost all manufacturers suggest going to either a 70 or even a 60° nozzle when increasing the pressure at the fuel unit?
Spread that fuel out at a higher pressure if YOU'D like to. Me, I'll follow what the makers say and be home having dinner while you go out on fouled head and coked retention ring calls. Chris0 -
huh
I thought with an increase in pressure the fire gets elongated, skewed from the original angle. ex. 80 degree becomes more like a 60 degree at a higher pressure.0 -
Not true according to Delavan, JMC
http://www.delavaninc.com/pdf/Fuel_Nozzles_for_Burners.PDF
From page 4, "After a true divergent spray is established, any increase in the pressure does not change the basic spray angle. In the above photographs it will be noted that the spray angle
measured at the orifice is the same at 300 psi as it is at 10 psi."
An interesting read.0 -
Agreed...
Good read0 -
They spec a different
nozzle (as told to me) because, while the angle does not change, the distance it is thrown will. The angle change is require to prevent the flame impingement0 -
pressure increase, angle increase
i would tend to agree with that too. higher pressure will create higher turbulence which will fan out the spray pattern more.
BUT that might not really happen with relatively small pressure changes. happens but not really noticeable.0 -
Check the article linked above
It's by Delavan's engineers accompanied with photos of the same nozzle under varying pressures. According to them and the pictures, there's no significant angle change with pressure change "after a true divergent spray is established". The information shows no angle change from 10-300psi.
Pretty interesting article that I'd recommend reading.0 -
Higher fuel
unit pressures will not change the pattern close to the nozzle. However, the angle of spray further away from the nozzle starts to pull in. From NORA Tech Guide Chapter 5 Page 83.
Many contend that results in a shorter flame.
Yes,
The Delavan article also mentions differences in pattern at higher pressures as the fuel spray gets farther away from the nozzle and the droplets begin to lose their momentum.0
- 120 Geothermal