u- value
Boilerpro_5
Boilerpro_5 Member Posts: 407
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=393&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
  • Mark_7
    Mark_7 Member Posts: 123
    u- value
    Anybody know the u-value of a 16" stone wall. Doing a heat loss on an old farm house. And there is nothing listed for that type of buliding.
  • Boilerpro_5
    From ASHRAE Fundamentals
    Limestone or sandstone is about 0.08 k value or at 16 inches, R= 1.28. Just remember that high mass structures like this respond very slowly, so when you hit design lows outdoors, it will take about 96 hours for that low temp to finally hit the inside surface. Also, they carry heat up fromthe ground, so the wall stays warmer than a frame wall. All this means is that you can keep equipment much smaller and still heat the home, assuming no setbacks.
    Boilerpro
  • Brad White_185
    Brad White_185 Member Posts: 265
    Bingo.
    Boilerpro nailed it, not just on the technicals but on style and artistic interpretation.
    9.9's across the board with China abstaining.
    EDIT: The 1.28 is correct for the stone portion at 0.08 R per inch.
    However, the indoor air film and outdoor air film (0.68 and 0.17 assuming a 15 MPH wind) will add another 0.85 R value just for showing up. Thus as a practical matter, the assembly R-value would be 2.13.
    The corresponding u-factor would be 0.47. I have glass in my house better than that, but the mass helps.
  • Rick Kelly_4
    Rick Kelly_4 Member Posts: 14
    To directly answer your question, the U-value would be 0.781