Baxi Luna HT380 - Operate DHW only
Options
Dan_51
Member Posts: 7
Installing a Baxi but the radiant portion of the job is not ready but there is a need for DHW right away. Has anyone plumbed in a Baxi to run DHW only? What is needed for the radiant supply/return lines and filling the system?
0
Comments
-
It makes DHW
via a plate HX inside. So it would need a loop from supply to return, on the boiler side, expansion tank, etc.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Yes you can
Just close the heating ball valves underneath, fill the boiler to 1-1/2 bat and let her go. You will use the drain valve on the right hand side to purge that loop of air.
Good luck...0 -
Hot Rod
Hi Hot Rod, it has an internal loop already. No need to have supply and return lines connected.0