Btu's of flowing water
Glenn Sossin_2
Member Posts: 592
I made this chart up a while back. It should help you. It uses the generic 500 value for water (8.33lbs x 60min/hr)
Flowing water Btu formula
What are the formulas for lets say a 10,20, or 30 deg temp drop /or temp gain of flowing water at say 1 gpm. Paul0 -
Q = 500*gpm*delta T
The 500 is assuming you're pumping 100% water. The number reduces to 490-480 depending on concentration of glycol.
Delta T in F.0 -
Specific heat
And the 500 is multiplied by the specific heat of the solution (based on glycol manufacturer supplied numbers). Water is 1 btu/lb-°F. 50% Dowfrost solution is 0.85 btu/lb-°F.
The 500 comes from water weighing 8.33lb/gal multiplied by 60 min/hour.0 -
Paul, here's one I use when I need to figure out the flow rate for a zone at variuos delta t's Zone's BTU's divided by 500 divided by the delta T desired = the zone flow rate.0 -
wrong attachment
Sorry attached the wrong file. This is an excel sheet that lets you plug in various flow rates, delta t values, etc.0