EDR for radiator
kpc_14
Member Posts: 38
size. Using the Burnham Heating helper and Dan Golden rules book...I would estimate that @ 4 edr per section or 68 for the radiator....kpc
EDR for radiator
I was wondering where I could find the EDR for a Kewanee steam radiator?
Thanks,
Phillip0 -
dimentions?
give us l x h x w...# of sections0 -
Each section is 9", wide 30" tall, 1 3/4" thick. Total radiator length is 42" and 17 3 tube sections.
I couldnt find this rad. in my Every darn radiator book, if I find one similar with close dimentions, will that work?0 -
Thanks for the information. This a pretty radiator, I sandblasted it to bare metal and painted it, I couldt believe the detail after sandblasting.0 -
radiator pix
how about showing some pix of your rad?--nbc0 -
Ok, I will try to post these , I hope it works!0 -
That's a column-type radiator
and it's a beauty! Nice job on the cleanup and paint.
The closest height in my chart is 32 inches, which would result in a capacity for each "3-column, 32-inch high" section of 4.5 square feet EDR. So the total would be 76.5 square feet.
You can use almost any column-type chart in "E.D.R." for these. Examples are American "Rococo" or U.S. "Florentine". The one you can't use is for H.B. Smith rads, they were different.
- 50 Industry Classes
