sizing main air vents
Options
Steamhead (in transit)
Member Posts: 6,688
two Gorton #1 vents on the shorter one, and one Gorton #2 on the longer one. The #2 is the fastest steam main vent made today.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
One main is 2 inch pipe and runs 24 feet before it reaches the last radiator on its run then it reduces to 1 1/4 inches for a 21 foot dry return.
The other main is 2 inch pipe and runs 40 feet before it reaches the last radiator on its run then it reduces to 1 1/4 inches for a 36 foot dry return.
Each main/dry return run has only one vent which is at the end of the dry return before it drips to the wet return. I can't make out the size of the current vents but they are raised 6 inches above the returns on 3/4 " nipples.
What would be the correct size vent for each supply/return loop?
Ideally should the vents be at the end of the main supply before it reduces to the dry return?
Thanks
0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements