Energize Taco 007 through end switch?
ata
Member Posts: 3
007 circulators are rated at 0.71 amps....
Can I do this?
I want to power a Taco 007 through a Honeywell V8043 end switch.
Can the switch handle the load?
Thanks.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
There should be
A voltage/amp load on the valve and a rating on the pump. If not try Honeywell.
You can add an isolation relay and know it will work.
Good luck0 -
Yes
Just discussed this with HW last week
I know end switch is line voltage rated
depends on the FLA rating of the Taco 007. If FLA is greater than end switch rating then don't do it. If you do use it, it has to be ran with bx cable or something with approved connector.
Rocky0 -
Yes0