Cast iron baseboard installation question.
bill nye_3
Member Posts: 307
Bottom -Bottom is the most common method I have seen and probably the easiest. It also allows for the coin vent to be installed on the top tapping and the end cap fits better.
Are you using mono-flo or series loop? In series the first rad will be hot and the last may be cool. I did a new house where I home-runned all the cast iron to a manifold with pex and added a couple of non-electric zone valves
I am a fully licensed plumbing and heating contractor from RI not a D. I. Yer. I am about to tackle a small job within an Historic building. This job has a call for cast iron baseboard. This baseboard is not going to be heated with steam, the heating media is water. I am aware of fan coils being piped different for steam and hydronic.
With in this multiple section loop. Considering the water flow direction Should I pipe each individual section of baseboard in on the bottom and out on the top?
Thanks for any help you may provide.
Russell L. Hill Jr.0 -
pipe from
bottom to bottom. The top taps are used for manual venting of air with 3/4"x 1/2" bushings and 1/8" key vents usually.0 -
Science Guy
Thanks for the revelation Ill split loop the system. Honestly did not think about the coin vent, just the big float vent so dismissed it. Thanks again
R Hill0 -
KF
Thank you see above ( Science Guy ) same applies to you. you have my e-mail any time I can be of help don't hesitate.0 -
Cast iron baseboard piping whats your thought? A lively experim
OK Ladies and Gentlemen.
The answer that I have received is bottom to bottom but you need a vent. ( with regard to Hydronic cast Iron baseboard piping). In my original request for input I entertained the thought of bottom to top piping.
I feel that this in effect would eliminate the need for a vent. What is your take?
Please let us have fun with this one after all we all have to pull the wrenches out side this WEBB site, Dont we!
Thanks to all!
RLHJ
Bottom-top
Sure Russell, as long as the top tapping pipes DIRECTLY UP to another radiator where the air can be vented....THINK!!0 -
purge
I obviously/honestly was thinking on the purge side of things your rite. Thanks but even with a vent would bottom to top piping utilize more of the radiator/baseboard on an overall bases?
RLHJ0 -
Top Tap
No! Hot water rises. Don't try to argue with "The Dead Men"0 -
Ain't it Great
As complicated as we try to make things it was simplified years ago if we care to observe and pay attention.0 -
cast iron baseboard
check out burnham.com go to technical information click I&O manuals then click baseboard and radiators then click on baseray then click installation manual.
that should answer any questions.
no arguement just exploreing0 -
I'm sorry
I wasn't around but I was around just not listening!0 -
DU what was I thinking!0 -
in our life time there is going to come a time that we have to disagree with the dead men! baseboard is no longer going to be like it is today, it is going to be more like towel warmers and radiant hanging on a wall. then what do you thing the answer to this question would be? I think it would be more like a fan coil. my reasoning is that there must be a point where the heated water needs to be drawn to the top in order to be most efficient! just an Idea and opinion0 -
Russel
It seems oyur are thinking like copper finned tubing and cast iron baseboard is a different animal. Its flow has a higher resistants than copper fin.
You want to use scoop tees to provide each section with as close to the same water temp. as possible. Remember the mass of the cast iron will suck up the BTU's quickly. Also the cast iron does not lend it self to purging, your going to want a coin vent on each section.
Balancing is also big here. You want to get even flow to each section.
I'm a big fan of scoop or monolfow tees for cast iron baseboard and keeping the sections to ten feet before dropping to another set of tee's. Also see if a reverse return piping set up will work here.
Next to radiant this is the best style of heat but it has to be done differently than copper.
Scott
Scott
Thanks I know what you are saying. this is a twenty nine foot heat loop total 14800 heat loss I was thinking of splitting the loop but mono-flow tees are very possible and easy to do, as I was reading the fist few sentences. I thought of reverse return piping it. it really has been such along time sense Ive had something to sink my teeth into, I forget .
Thank you for your support
RLHJ0 -
Should dielectric unions be used if CI basboard radiators are piped using copper tubing?0 -
no , male adapters or union els
Should the male adapters or union ells be dielectric?0 -
No don't worry about them. There's really no fresh water makeup on a hydronic system so you won't see corrosion.
- 85.7K THE MAIN WALL
- 49 Biomass
- 72 Chimneys & Flues
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 848 Plumbing
- 5.8K Radiant Heating
- 372 Solar
- 14.5K Strictly Steam
- 50 Water Quality
- 39 Industry Classes
- 15 Recall Announcements
