Time for a vaporstat?
SpeyFitter
SpeyFitter Member Posts: 422
I am thinking of getting one too, and plan to mount the gauge on a tee with the vaporstat, after the pigtail. Should keep the steam out of the diaphragm.
Meanwhile, any opinions on vaporstats L408A1132 (mercury switch) vs. L408J1009 (snap-action switch, mercury-free)?
I just don't like snap action after problems with two PA404 pressuretrols...
-Charles
  • Marc_13
    Marc_13 Member Posts: 1
    Time for a Vaporstat?
    I have a one pipe steam system, well vented mains, new valves on the radiators and despite all this I am still hearing some strong venting from the rads on the second floor. I have a Honeywell pressuretrol 404a model which I am told is not too accurate. Its set at .5/1.5.
    TIME FOR A VAPORSTAT?
    Is all this strong venting due to the fact that this pressuretrol is perhaps not giving the system the pressure set but rather something higher??
    Thanks...................
  • Gary Segal
    Gary Segal Member Posts: 37
    I'd first buy a
    low pressure gauge to see what is really happening, vefore taking the plunge on a Vaprostat. Here is a link to a 0-3 psi gauge; there are may other choices on the website.
    http://www.gaugestore.com/prodinfo.asp?number=33020
  • JohnG_3
    JohnG_3 Member Posts: 57
    Max temp on those gauges
    Those WIKA gauges have a maximum media temperature specification of 140 degrees F. Yet people here are using them successfully. Are the gauges okay for steam?
  • Tom Hopkins
    Tom Hopkins Member Posts: 554
    snap action may not be a function of
    your Pressuretrol, it may be a response to something that is happening in your boiler. I know my vaporstat can get very violent if the water level is too high.
    Additionally, it seems that there is a certain pressure range where it gets jumpy. Since my low pressure gauge (on the same pigtail) jumps when the vaporstat jumps, I am pretty confident that the problem is not with the control, but with the behavior of the system.
  • marc_14
    marc_14 Member Posts: 2
    Thanks for the comment.
    How would I attach. I currently have the code guage on a short 2" straight pipe with a 90 degree elbow.
  • Boilerpro_5
    Boilerpro_5 Member Posts: 407
    Installation location...
    You may want to consider putting the Vaporstat either on the end of the steam main or up on the header piping. In these locations, you tend to get away from the pulsing inside the boiler that will drive the vaporstat crazy. It has worked for a number of steam gurus here, I understand. Haven't yet tried it myself, though.
    Boilerpro
  • mark_109
    mark_109 Member Posts: 3
    How would I attach a second guage off the first.
    Thats what I was asking.
    Thanks
  • mark_109
    Thanks
  • Charles_8
    Charles_8 Member Posts: 74
    Snap action
    I wasn't referring to that kind of jumpy behavior, but to a tendency for the actual cut-in pressure to keep "drifting" lower (over several weeks) until the boiler will no longer fire after cut-out, even after the pressure has dropped to zero! This has to be a mechanical problem in the linkage since the screw adjustment, pointer scale, and differential wheel do not move, and the pigtail is not plugged, but the setting is wrong...
    In fact I have removed the pressuretrol and applied (by mouth) small amounts of pressure and the diaphragm/switch do work, even though the pointer no longer indicates anywhere near the actual pressures when it switches.
    Of course, if the new mercury-free one uses the same mechanical innards and only a microswitch instead of a mercury switch, the difference is moot...
    -Charles
  • steve pajek
    steve pajek Member Posts: 28
    vaporstat????
    > TIME
    > FOR A VAPORSTAT? Is all this strong venting due
    > something higher??
    sounds like a venting problem not a pressure problem. what are you venting the mains with, and the second floor radiators?
  • Tom Hopkins
    Pictures of gauge installation
    Mark, hopefully these pictures will explain the install. I do not think the gauges get much above ambient temperature, even after an extended run.
  • mark_110
    mark_110 Member Posts: 2
    Thanks,now I understand it.