Chimney Liner Size
I am having a chimney liner installed in my 80-year old clay lined chimney. The chimney expert tells me I need an 8-inch liner. The length of the flue is 28-feet. The liner would be corrugated stainless 316-Ti with two bends to accomodate the flue passage above the fireplace.
To install the liner will require removal of the present clay tile lining, which will add to the cost and potentially require cutting a hole in our family room wall to access a bend in the flue that is behind a plasterboard wall.
The 8-inch size was based on the 7-inch vent pipe from my WM SGO-4 and the 3-inch vent from my Bradford-White Combicore 65,000BTU/hr water heater.
My boiler is under-fired at 1-GPH, so I was wondering if perhaps a 7-inch liner would be fine, instead of the 8-inch. This would be a total of 205,000 BTU/hour. This would allow the liner to be inserted without removing the tile lining.
I obviously want to do what's right, but wonder if the underfiring makes a difference.
Thanks!
Steve
  • Nick S
    Nick S Member Posts: 62
    Why do you need a liner? If the current chimney is in good shape, fire your boiler and water heater where they should be and you should be fine. If the chimney is falling apart and you need a liner, put in the biggest one that will fit.
  • Steve Garson_4
    Steve Garson_4 Member Posts: 4
    The chimney needs a liner. The clay is deteriorating and some of the mortar has fallen. I also want to convert the boiler to gas. As it is today, the 65K BTU gas water heater is damaging the chimney.
  • bob young
    bob young Member Posts: 2,177
    fuel gas code
    verify load capacity as per n.f.g.c. got a feeling you are well within limits with seven inch. chimney liner guys are not engineers. i could be wrong but it is worth researching.
  • Bob Harper
    Bob Harper Member Posts: 1,123
    You need a Level II inspection of the chimney to ascertain if it needs a liner or not.
    In this case, since you already know it has damage and you're venting higher efficiency equipment, you will need a liner. There is a lot of info. you need to size it you have not provided. However, as an example, if the boiler is rated at 84% steady state efficiency at 1.5 GPH with a 4 ft. lateral offset and 25ft. height, a 6 inch liner should do. Now, derate the liner for the offsets and still a 7 inch liner should do.
    Get another chimney lining contractor's bid.
    Bob
  • Keep in mind that
    liners have 20% less capacity than a type B gas vent when doing calculations.
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,577
    If
    You're converting to gas anyway,use a mod/con and forget the chimney altogether!
  • allan_7
    allan_7 Member Posts: 55
    Spec Chart
    Flex-L International 614-895-8948 Charted Values:
    6" @ 25' Class B Connector Fan+Fan 270
    Fan+Nat 221
    Nat+Nat 198
    Single Wall Connect Fan+Fan 262
    Fan+Nat 214
    Nat+Nat 192
    6" @ 30' Class B 289 238 213
    Single Wall 280 229 206
    7" @ 25' Class B 409 341 268
    Single Wall 398 332 261
    7" @ 30' Class B 438 367 288
    Single Wall 426 357 279
    Tables reflect 20% de-rate from B-Vent Tables.
    Most oem's recommend using the smallest liner possible, rather than oversizing (condensation, wet-time issues, etc.
    Recommend Class B-1 double wall connectors for gas equipment.
    Hope this helps....
  • allan_7
    Spec Chart
    Fan+Nat 221
    Nat+Nat 198
    Fan+Nat 214
    Nat+Nat 192
    Hope this helps....
  • allan_7
    Spec Chart
    Fan+Fan 270
    Fan+Nat 221
    Nat+Nat 198
    Fan+Nat 214
    Nat+Nat 192
    Hope this helps....
  • Rich Kontny_3
    Rich Kontny_3 Member Posts: 561
    Why don't
    You save that money and install a closed combustion boiler that vents out the side of your home? Size it for an indirect water heater and you have one gas fired heat source with no need for the chimney. This way you would have an updated heating system with energy saving capabilities.
    If your liner is usable and safe I would not waste money on it if you plan to upgrade in he near future. Might even be some utility incentives $$$ call and find out. Don't rush into the chimney liner project (unless it is unsafe) until you have options and perhaps second opinions.
    Rich K
  • Joe Brix
    Joe Brix Member Posts: 626
    If you're getting a new boiler
    I agree, just get an indirect HW heater. A smaller 5 or 6"
    liner might be all you need for the single gas boiler.
  • Buzz G.
    Buzz G. Member Posts: 61
    Lining old chimney
    is expensive. I had this same problem and my chimney was not even clay lined. The solution chosen was Knight condensing boiler with IDHW (W-M) and using one 3 inch PVC for vent and one for combustion air -- and running those up chimney. It was a lot less costly than lining chimney and staying with gas HW heater and more efficient too. Have not looked back after making this choice.
  • Steve Garson_3
    Steve Garson_3 Member Posts: 10
    It's a steam system.
  • Paul Fredricks_3
    Paul Fredricks_3 Member Posts: 1,556
    I looked at a house the other day. It had a Smith boiler with a 7" flue connection. Someone at sometime had installed a 5" liner. Per the calculations, the 5" would work. But we called Smith and they said the smallest you can put on their units is 1" smaller than what it came with.
    When in doubt, call the manufacturer.