Taco outdoor reset control
Joe Mattiello
Member Posts: 748
The Taco PC700-2 will modulate the boiler to deliver the water temperature required to satisfy the load, based on outdoor temperature. However, if you have a non-condensing boiler the PID microprocessor has to start the curve from the minimum operating temperature typically set at 140 degrees. Youre saving are greater when using a condensing type boiler. Obviously, anytime you can reduce the water temperature of the boiler, you will save. How much is the variable.
Joe Mattiello
Taco Comfort Solutions
installing Taco outdoor reset control
I have a pretty new boiler with 6 zones and a Taco 6 zone switching relay control. It looks like I could install a Taco PC700 outdoor reset control which would vary the boiler temp based upon outdoor temp. There are some other options, such as a purge control that pushes all the hot water to the priority zone when the burner shuts down. Are these add on controls cost effective?0 -
or go with Buderus Logamatic
Since this is a Buderus boiler I could go with a Buderus Logamatic control or a Techmar I guess.0 -
Taco Reset
I don't install Buderus but I install many of the Taco 700 controls, they are simple to install and there is no wiring exept for the sensors, you are generally going to have a switching relay anyway. I have yet to return to any job I have installed one for a problem. I'm sure the Logamatic is a great control and has a lot of great fuctions, most of the jobs I do would never utilize most of the functionality of that control.
C0 -
Take a look at our new Aquatrol unit
We offer outdoor air temp based reset, 4 zone modules that will accept either pumps or zone valves, true priority for an indirect, communicating thermostats and a host of other cool features at a very competitive price. All packaged in an attractive black & red console that is VERY easy to wire and service. Programming is very simple, and once set up, will not be lost if the power goes out. This is just the start...much more coming soon. For more info, go to www.honeywellwaterawareness.com0 -
Bill
you need to add an e in awareness.
Jack0 -
Thanks for catching that.
I fixed it!0
- 119 Chimneys & Flues
- 76 Pipe Deterioration
