Converting old Electrozones to Honeywells..hot water system
DWB
Member Posts: 2
I'm a plumber w/ limited heat and wiring experience. I'm replacing 2 old electrozone zone valves and the manifold below them to new Honeywell zone valves. Small boiler, 3/4 inch valves, and I think the gas valve is millivolt. Do I need a special relay for the conversion? Not sure if this is enough info, but any feedback would be appreciated.
Zone valves
There are four wires or terminals (dependind of choice of model) on the Honeywell .The two yellow wires are to activate motor. The two red are a end switch. When valve fully open it trips the end switch. The end switch goes to TT on a relay which engages cirulator and if set up this way ,will also turn on burner.The relay of chioce would be A double pole .One set for 110v circ & a second for milli volt burner or even 24v model.
The wiring for zv motor...Transformer -thermostat(RH-W)-thermostat-one yellow lead ZV-other yellow lead -to other side of transformer.
To size transformer find amp draw on zv .I think are .3 A .mutiply by voltage which is 24V equals VA transformer needed... Say 6 valves 6x.3A x24V is 43.2 VA. use 50VA transformer for the bunch
Hope this helps but does not confuse....0