Yellow soot
Patchogue Phil_29
Member Posts: 120
It's not underfired that I am sure.
OK, what are the lowest limits that this unit could be set to? I know it is difficult to say w/o taking readings.... I am just curious as to a ballpark figgure?
Yellow soot
What causes yellow soot in the flue of an oil fired boiler?
High sulphur content
in the oil?
What are your combustion test readings?0 -
The unit has been condensing, you find this alot in "cold start" boilers.
Leo0 -
Not a cold start
It's a single pass New Yorker S-AP boiler with standard Beckett gun.
Could this happen with this setup from lowering the limits too much in the summer?0 -
Read the boiler manufacturers instructions....
If they are still available.... and if not, make provisions for a system bypass.
Cold return temps are the most likely culprit, find the preferred way to avoid them. Chris0 -
Limits too low or putting to small of a nozzle from what is speced. If none of these try the by pass piping that was suggested.
Leo0 -
Excess air!
It's from unburned fuel in the fluegas. You're operating on the Lanthier Scale as opposed to the Shell-Bacharach Scale. Need to adjust with an ohmmeter and get 'True Zero' smoke, FACT!
BTW, you can also get to the right place by tuning for minimum CO, not highest CO2.0 -
If you're below
75% of the maximum firing rate you're underfired as per ASME Section IV.0 -
I meant triple aquastat settings.
Typically
You don't want the circ running on older style boilers unless the boiler temp is above 140* to be safe.
I'd also suspect garbage fuel with a high sulfer content.
Or condensation in the flue caused by A: low boiler temps, B: improperly tuned burner, C: burner end cone dirty or worn affecting the flame pattern,Draft problems of one sort or another.
what is causing yellow soot in my oil furnace heat exchanger
i have a new armstrong horizontal oil furnace Mod# LHR80C57/72D12 . my first one cracked the exchanger in about 7 years. this one is only 3 years old and is showing signs of what looks like sulphuric acid in the smoke pipe and heat exchanger. small damp yellow spots that turn to powder when i brush them. i have only seen this in gas flues in the past. the chimney is a healthy 8" terracata and my smoke stack 6" pipe 10' long with one 90. im running the .50 nozzle which is the correct size for this burner. Is it the stack temp. not getting high enough?0