Slight oder from gas valve
David Hohengasser
Member Posts: 52
While obtaining the model number off my Honeywell gas valve, I noticed a slight gas oder from the on-off-pilot knob. I can smell it with my nose touching the knob, but if I back off 2" there is no smell. Is this OK? Natural gas. Model# V800A 1310. Regulator V5306A. Operator V804A.
Take a soap and water mixture
and a brush and apply to the valve just stay away from electrical connections. Then look for bubbles. It could be leaking from around the pilot adjustment screw or the regulator cap.
There should be no smell of gas at your valve.0 -
Gas valves are made of cast aluminum, which is porous. That means that there's going to be a slight gas odor to any valve that's had gas go through it. There's no harm in that. The important part isn't the odor but whether or not there's a leak when it's in operation. Tim's right about how to test with bubbles.
Bubbles remain the best way to test--even better than gas sniffers which can easily be set to be too sensitive and scare the sh-- out of everyone unnecessarily.
It has been my experience
that gas valves typically do not have an odor present unless there is a leak. Granted if you remove a gas valve and smell the inlet or outlet the residual mercaptan odor is there.
I like to reference a paper that Honeywell printed several years ago that explains the rash of complaints of gas valves leaking that took place in the late 1980's because of the use of certain "sniffer" type detectors which were calibrated to pick up very low levels of methane. These were used to test for cracked heat exchangers on warm air furnaces. I apologize for the length of this but I think it explains gas valve leakage very well.
THE TRUTH ABOUT GAS LEAKAGE COMPLAINTS AND GAS VALVES
BY Honeywell
Complaints of gas leakage through regulator vent openings have become increasingly common in the last few years. This rise in complaints is not the fault of gas valve manufacturers,rather the problem is more commonly the result of modem furnace design and a trace leakage phenomenon that can be found in all gas valves. Because these factors are not widely understood and the wrong tools are often used to diagnose gas leakage, gas valves are being replaced unnecessarily.
This paper briefly explains how modern furnace design contributes to leakage complaints, presents the results of laboratory testing done by Honeywell to confirm valve integrity. and suggests a more reliable method of verifying actual leakage than is currently being used.
MODERN FURNACE DESIGN AND LEAKAGE COMPLAINTS
The recent rise in the number of gas leakage complaints involving gas controls appears to be caused primarily by how newer furnaces are vented.
Since January 1992 all furnaces are made with induced draft blowers and all boilers are made with vent dampers or induced draft blowers. The result of this design is that any gas remaining in the burner is trapped when the gas valve shuts off, since it cannot easily move up a vent tube to the outside air.
This residual gas tends to slowly dissipate in the space around the appliance, and, depending on the location of the appliance, is sometimes noticeable to the occupants who become concerned about the gas valve as the source of the gas odor.
When the service technician arrives, testing is commonly performed using an electronic gas detector. If the detector senses gas at the valve, the conclusion is that the valve is defective.
LABORATORY TESTING REVEALS TRACE LEAKAGE PHENOMENON
Most of the valves returned to Honeywell for testing related to this phenomenon were the result of a technician using an electronic gas detector. Gas valves returned to Honeywell as the result of leakage complaints were tested as follows.
Returned gas valves were tested for leakage on air at 21 in. wc test pressure using a Bubble-O-Meter flow meter with a sensitivity of less than 5 cc/hr. There was usually no indication of leakage on the flow meter, and it was concluded that any leakages were therefore less than 5 cc/hr.
Following this flow meter test, gas valves were set up on a gas burner and cycled with natural gas. After cycling on and off, a TIF 8800A Gas Detector was used to sniff for gas leakage. The gas detector consistently indicated the presence of gas at the regulator vent cap and the main burner orifice. This indication was still evident as long as one hour after the gas control was shut off.
To further verify that no significant gas was leaking through the regulator vent cap, the cap was removed and a thin film of liquid soap solution was formed across the vent opening. The valve was again cycled on and off. As the valve cycled, the soap film expanded and contracted slightly, but did not grow or break.
The presence of gas as detected by electronic gas detectors was reproducible on other Honeywell valves and competitors' valves and can only be attributed to gas leaking through the valve diaphragms.
This trace leakage phenomenon (less than 5 cc/hr) has been reproduced on Honeywell VR8200 and VR8300 Valves as well as valves manufactured by White Rodgers and Robertshaw that use various rubber compounds and fillers for the valve diaphragms.
Although the permeability values for gases through rubber diaphragms is extremely small (approximately 0.56 cc/hr) and almost negligible when compared to the 200 cc/hr maximum allowed by ANSI (ANSI allows 200 cc/hr for outerwall gas leakage and 235 cc/hr for valve gas leakage), it appears this is enough to explain an instantaneous indication of gas from a sensitive electronic gas sniffer detector.
RESPONDING TO GAS LEAKAGE COMPLAINTS
To respond effectively to gas leakage complaints, service technicians need to take a two-step approach before identifying the gas valve as the problem:
First, they must identify the presence of gas by using a reliable gas detector. And second, they must verify that the flow of gas coming from the valve is unacceptable by using a reliable flow meter.
If gas is present in low concentrations as the result of furnace design and the trace leakage phenomenon, replacing a gas valve will not solve the problem. They must educate the appliance owner about the source of gas odor and assure them that it is both safe and normal for that appliance.
SUMMARY
Gas appliance manufacturers are aware of the problem of residual gas venting into the area surrounding the furnace and are working to reduce it. There are tradeoffs, however, in allowing more venting. With current test procedures, more venting after shutoff tends to reduce the efficiency of an appliance.
Honeywell encourages manufacturers to select newer designs to reduce the presence of unburned gas around the appliance and thereby reduce the number of leakage complaints.
Until a solution is found for venting this residual gas, it is important that service technicians know how to correctly identify and test for gas valve leaks and that they be able to educate the consumer about the presence of gas odors. While a gas sniffer is useful for detecting the presence of gas, it is not a measurement device for actual gas flow.
My comment, a properly set up Combustible Gas Indicator set to measure propane or natural gas in the LEL range (lower explosive limit) 2.15% for propane and 4.5% for natural gas will not detect 200 cc/hr or 235 cc/hr and definitely not .56 cc/hr. Therefore you would not be smelling gas from the gas valve but in relation to this paper from Honeywell explaining this phenomenon.0
- 50 Industry Classes