Erratic Pressures
Eddy
Member Posts: 21
I've got a 2 loop hydronic system. The primary circs the boiler loop and the secondary circs the building loop. They are tied together with a 3 way mixing valve. The valve modulates for a constant 140 deg return to the boiler (cast iron sectional). Static fill pressure is 12 psig. When the system runs the pump pressures are anywhere from 10 psig to 50 psig on the suction and 25 psig to 70 psig on the discharge. The boiler's operating pressure is 50 psig. So, the safety valve on the boiler dribbles when the suction gets near 50 psig. Why aren't my pressures more constant? It does not appear that the position of the 3 way valve has any affect on the pressures. I have the same problem with the chiller loop which also has a 3 way valve for the cooling coil.
Are my compression tanks (bladder type) not working or maybe plumbed wrong?
Assuming the job
is piped correctly - it sounds like the valve(s) CV is not matched to the pump(s) capacity. I would get out the specs for all pumps & valves & give them a double check.
okay
Please give us a cheesey little drawing of the piping layout.0 -
Burner off
I would check pressures with the burner off and the static starting at 12 psi on all the gauges. I would make the pumps run and see what the pressures are with no heat. If they go up as you say you must have pumps with tremendous head. If they don't then you have a air cushion issue in the expansion tanks.0 -
That could take me a few days but i'll give it a shot.0 -
be waiting
thanks0
- 120 Geothermal
- 169 Indoor-Air Quality
- 396 Solar