backflow preventer vent dripping
Jim_47
Jim_47 Member Posts: 244
When the boiler side of the device has a higher pressure than the supply or house side pressure.
the device will allow any excess to go to the drain instead of backing up into the domestic water system.
  • antonio
    antonio Member Posts: 2
    backflow vent dripping
    What causes a backflow vent to drip? High inlet pressure or boiler side pressure exceeding the inlet pressure?
  • Shane_2
    Shane_2 Member Posts: 200
    I usually see them drip if I shut off the water main for a plumbing repair, so that would mean it was doing its job when the boiler pressure is higher than the house pressure.
    Shane
  • antonio
    Thanks guys. Thats how I though it worked, just wanted to make sure before I call my customer. He actually mentioned something about house pressure to my installer so he may have a pressure problem in the home.
  • a bit blowing off there
    can be normal due to occasional, pressure differentials, but a drip-type leak there is indicative of a leaking disc and piston assembly/o-ring/seat etc, and they're easily rebuildable
    i certify and/or rebuild them
  • Antonio
    RPZ's spit or drip when the inlet pressure drops below the outlet pressure. Not an uncommon occurance as fixtures are used or water main pressure drops in the street and an interior draw occurs allowing the lower street pressure to be seen by the RPZ PRV. The best way we've found to eliminate that issue, is the installation of a soft-seated check valve on the inlet side of the PRV, which traps the highest inlet pressure to maintain the pressure differential required for spit-less RPZ operation.
  • Tilmon_2
    Tilmon_2 Member Posts: 2
    To remedy a driping vent on a backflow preventer I begin by cleaning it, if that doen't work I install a check valve upstream, and if that doesn't work replace it. ( this is for residential type "watts 9D" backflow preventer)
  • drip or spit?
    Watts Trouble Shooting Guide - Backflow Preventers
    Problem Cause Solution
    for a spit, watts says;
    A. Valve spits periodically from the vent.
    A.1 Fluctuating supply pressure.
    A.2 Fluctuating downstream pressure.
    A.1 Install a soft seated check valve immediately
    upstream of the device. (Watts 3⁄4" - 2" No. 601
    bronze valve.)
    A.2 Install a soft seated check valve downstream of
    the device close as possible to the shutoff valve.
    (Watts 3⁄4" - 2" No. 601 bronze valve.)
    for a drip, watts says;
    B. Valve drips continually from the vent
    B.1 Fouled first check.
    B.2 Damaged or fouled relief valve seat.
    B.3 Relief valve piston o-ring not free to move
    due to pipe scale, dirt or build up of
    mineral deposits.
    B.4 Excessive back pressure, freezing or water
    hammer has distorted the second check.
    B.5 Electrolysis of relief valve seat or first
    check seats.
    B.6 Valve improperly reassembled.
    B.1 Flush valve. If flushing does not resolve problem,
    disassemble valve and clean or replace the
    first check.
    B.2 Clean or replace the relief valve seat.
    B.3 Clean, grease or replace the piston o-ring.
    B.4 Eliminate source of excessive back pressure or
    water hammer in the system downstream of the
    device. Use Watts No. 601 to dampen out back
    pressure and No. 15 to eliminate water hammer.
    Replace defective second check assembly. In
    case of freezing; thaw, disassemble and inspect
    internal components. Replace as necessary.
    B.5 Replace relief valve seat or inlet cover. Install
    dielectric unions (Watts series 3001 through 3006).
    Electrically ground the piping system and/or electrically
    isolate the device with plastic pipe immediately
    upstream and downstream of the device.
    B.6 If valve is disassembled during installation, caution
    must be exercised to install check springs in their
    proper location.
  • mtfallsmikey
    mtfallsmikey Member Posts: 765
    Did you
    go ahead and rebuild the RPZ?...always a good idea..get the relief, 1st and 2nd checks..also test (and record the results!)
  • Al Corelli_2
    Al Corelli_2 Member Posts: 395
    Backflow Drip
    We do what Tilman does. Each install gets a swing check before ANY backflow device.
    Really keeps those "my new boiler is leaking" calls from happening.
  • Eliminate the problem altogether
    After so many jobs with leaking 9Ds , we switched to a ventless backflow preventer for our residential installs .
    Is a vented backflow a requirement in most places ? If so , why ?
  • IPC 608.16.2
    connection to boilers sez;
    The potable supply to the boiler shall be equipped with a backflow preventer with an intermediate atmospheric vent complying with ASSE 1012 or CSA B64.3. Where conditioning chemicals are introduced into the system, the potable water connection shall be protected by an air gap or a reduced pressure principle backflow preventer, complying with ASSE 1013, CSA B64.4 or AWWA C511.
    why vented?
    in the event of failure for whatever reason, the water can be safely discharged
  • Thanks Mike
    for the excerpt .
    Although the vented backflow seems like overkill if you have that and a PRV on the makeup water pipe . Just thinking about what would have to happen ........ the pressure on the house side would have to be very low or nil , and the PRV and the ventless backflow would both have to fail and let water flow in the wrong direction ..... at the same time .
  • my pleasure
    and part of the concern is where, under the right conditions, boiler chemicals can be 'pulled' back into the city main, and potentially contaminate the neighborhood etc
    and if you can locate, or maybe download them, check out the spooky stories in the EPA's cross-contamination control manual, and/or the watts regulator's pamphlet.
    and in these litigious days............
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,580
    backflow substitute
    i stiil think my own [pre backflow regulations] arrangement is best and simplest [never needs a yearly $75.00 "tuneup"]--a spring-loaded shower valve for the makeup feed line into my one pipe boiler.
    i would think that most systems with an appropriately sized reserve tank could be filled with a hose [maybe from the hot water heater]once a season thus doing away from the necessity of having to have it serviced so frequently.
    speaking of epa horror stories have you ever had any experience yourselves? the HO is far more likely to be drinking water backing out of his sprinkler system than from his boiler
    i might add that of course i do have a backflow on my boiler, i just hate being required to install a seemingly unnecessary $500.00 item just because "mommy says".
    --nbc
  • amen to the
    filling it with a garden hose. i do the same meself. inconvenient but......
    hey, is your sis in sweeney?
  • mtfallsmikey
    My fav cross-connection story
    Someone adding water to a 55 gal. drum with Chlordane in Roanoke Va....no backflow preventer on the hose bibb, lost pressure, ALL of it got sucked back into the main...city had to replace about 1 mile of main...was the opening of the cross-connection certification class I did in '95.
  • yearly certs
    have become the norm, and law in some states, for many high risk environments
    something as innocuous as the fire dept flushing hydrants, can cause enough of a pressure drop, which can pull water from a near-by bldg's treated boiler or similar vessel, into the local supply water. firefighters leave, cooties stay in the supply system for the locals to drink