1972 american standard boiler 2B-J1 or A37 M-
Options
ken weaver
Member Posts: 2
i have a 1972 american standard boiler with a plate on that says A37 M and 2B-J1--what size (BTU) boiler is this thank you
0
Comments
-
american standard boiler
i have a 1972 american standard boiler with a plate on that says A37 M and 2B-J1--what size (BTU) boiler is this thank you0 -
838 steam square feet EDR
or 201 MBH on steam, 233 MBH on hot water. Firing rate with original burner 2.5 GPH, if you retrofit a flame-retention unit you can get the same input from 2.00 GPH.
This is one of my favorite older boiler series.0