re-pipe steam header
Options
kev
Member Posts: 100
Two 2" risers into new 3" header. I would like to place new header on opposite side of boiler from risers, giving me about 10" of horizontal pipe on each riser. Is there a max trouble free distance? This will also place the equalizer opposite to existing hartford loop. No need to change if I can pipe straight down from header and then over 10" to existing tee on loop. Would this create a problem? Thanks for your reply.
0
Comments
-
repipe header
you need 24 in hieght from water line to the top of the pipe0 -
yes
I will have that.0 -
repipe steam header
yo might want to condider a drop header on your boiler repiping looks cool0 -
But,
drop header or not, he's asking how long the horizontal legs can be before AFTER the 24" A dimension is achieved, before arriving at the header and equalizer, w/o trouble. I can see the piping in my head, just don't know the answer.0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements