baxi 310FI circulator question
Options
Tony_23
Member Posts: 1,033
it has 5 gpm @ 13 ft/hd available.
Not much if it's radiant.
Not much if it's radiant.
0
Comments
-
I'm trying to help a guy troubleshoot a boiler that is 200 miles away. Well I'm no radiant troubleshooting guru by any stretch. He is heating a 1600sq ft cabin. My question: is the pump that is factory installed in the baxi the only pump he needs in the system?0 -
Yes i think that's about right tony. I think you can use a system circ. and just do a injection off of the Baxi.the system circ will be sized for the radiant floor requirements.Pri/sec system.0 -
Call the BAxi guys.
They helped me out with one that is 7 years old, although they were a little tough to get in touch with sometimes. He told me the pump can push 1900 feet of 1/2 tubing. This job was not that large though.
Rob0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements